Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2805:53 PM. Last Modified: 2024-03-2603:09 AM
Hi,
No. A Back-UPS is designed to provide output when AC is not available. Also, The more deep discharges the UPS experiences the sooner the battery/batteries will fail so it is not a good idea to run on battery output for long periods of time.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2805:53 PM. Last Modified: 2024-03-2603:09 AM
Hi,
No. A Back-UPS is designed to provide output when AC is not available. Also, The more deep discharges the UPS experiences the sooner the battery/batteries will fail so it is not a good idea to run on battery output for long periods of time.