Can any ups provide above watt rating wo auto shutting off (when on mains ac power) ?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Can any ups provide above watt rating wo auto shutting off (when on mains ac power) ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:17 AM . Last Modified: ‎2024-03-27 01:05 AM

0 Likes
4
2032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:17 AM . Last Modified: ‎2024-03-27 01:05 AM

Can any ups provide above watt rating wo auto shutting off (when on mains ac power) ?

hi,

i have quite a few enterprise as well as consumer apc units in service due to my job (enterprise it and network support).  In these scenarios I would never consider overloading a ups beyond * 70% of its rated battery capacity.

HOWEVER,  my personal home PC rig has 3x 290x (amd) gpus, -  the rare times I play a high end game, my PC alone (no monitors, just PC) can pull nearly 1400w from the wall (I have a 1650w psu) - this will cause even a 1300w ups to start beeping and then shutoff (as designed, with no actual wall loss of ac power, just the ups auto shutting down due to overload) .

my Question is that 99.9% of the time I'm not playing a game and my PC alone will only draw between 250 to 300 W from the wall. So those are very rare times that I'm playing a game and drawing nearly 1300 W - if (during my rare gaming sessions) the main AC power were to fail  and my UPS batteries could not support that load, I'm totally fine with losing total power. However the 99.9% of the time that my PC is drawing less than 400 W I would like it to be protected from power loss (i.e. Web browsing , working or just the idle PC).   Given my scenario, short of spending nearly $1000 on a UPS, even spending $4-500 on a UPS causes more problems than it solves (as I do play games more often than my wall ac power fails.)

 I'm hoping there is some type of solution (or specific type of ups) that during an over wattage event, the UPS simply does not provide battery back up but also does not auto shut down (ie it functions as a normal power strip) .   Does anyone know of such a solution? Or perhaps a manufacture who's battery back up does not shut down in an over wattage scenario (but of course, it also won't provide any runtime during over wattage- or even better yet moves the auto shutdown logic to the battery inverter,  such that if you draw too much when the battery inverter is on/active then it shuts down versus shutting down if you draw too much from the wall, when the wall is clearly capable of providing that power (which is what your home breakers are for) )

 The only other solution I can think of is to look into some kind of quick AC transfer switch that allows me to bypass the UPS and go straight to the wall which I would switch right before I were to play a game (in other words the equivalent of shutting down the PC moving it to the wall starting it back up playing my game and when done  shutting down and moving the PC back to the UPS) 

 Although I don't agree with the reasoning, I do understand why UPSes auto shut down when you're pulling more than their rated battery capacity. So I'm not looking for an explanation of this logic but more so for any potential solutions to my pretty unique scenario ( IE, I need protection for the 99.9% of the time that my CPU draws under 400 W but at the same time a backup power source that does not automatically shut down when I'm drawing 13 or 1400 W for an hour or 2 , once every other month or so) 

Thank you!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

0 Likes
0
2030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

APC used to sell a device that would let you "hot swap" a UPS without cutting power to the attached load. I believe the model number is AP019. I don't know if they still sell anything like the AP019 as a current product. I think it would do what you want: let you run the computer with backed up power when you're not gaming and run directly from the wall outlet when you are. There is a manual switch right on the unit.

(Caveat: the AP019 I have indicates a maximum rating of 12 amps. At 1,400 watts you'd be running right up against 11.7 amps worth of current drawn.)

I'm not aware of too many UPSes that will let you overload them by any appreciable degree before they shut down. (The older CS350/500 models as mentioned previously are a good example of units that will stay on even if heavily overloaded. I believe that to be a lot of the reason why they were recalled.) And as you note, it's definitely not nice to push one right up to its limits. If you wanted your computer to stay up during power failures when you are gaming, I think the smallest suitable UPS APC sells would be the Smart-UPS 2200. While rather expensive if you were to buy one new, a lot of good used examples are free for the asking or very cheap when the batteries conk out.

Getting one of those would give you the advantage of a computer that stays up for hours when it's not being used for gaming purposes.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

0 Likes
0
2030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

I have an old BackUPS CS here that will scream blue murder if you overload it, but it keeps on supplying power. The beeping does get intolerable pretty quickly however.

Most sane UPS units I've worked with don't like being overloaded though. I picked up an AP7721 ATS that I interposed between a UPS and the IT equipment to allow me to perform maintenance on the UPS without disruption. Somehing like that'd do what you want. Alternatively an external bypass panel would be another option.

Personally I'd just go for a bigger UPS, but then I like lots of margin.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

Hello James,

Thank you for posting your questions here on the forum. Just so that I can get a better sense of what you have (and to make sure we are getting you something better), what UPS do you have?

What plug does it have? I am assuming based on the power draw, that this is on a 20A circuit, correct?

Also, I'm just curious, how are you tracking power draw and know that you are pulling 1400W?

I myself am a PC gamer, so I completely understand (but my rig is nowhere near as awesome as yours).

Thanks,
Shanon

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

I'm curious what Shannon comes up with, but just wanted to provide a bit of the bigger picture. What you want is reasonable, however one issue is that UPSes transfer to battery temporarily due to any disturbances on the line, not just power failures. This is because the UPS needs to react before attached equipment detects loss of power. Could be inconvenient if you're playing a game at the moment.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:18 AM . Last Modified: ‎2024-03-27 01:05 AM

APC used to sell a device that would let you "hot swap" a UPS without cutting power to the attached load. I believe the model number is AP019. I don't know if they still sell anything like the AP019 as a current product. I think it would do what you want: let you run the computer with backed up power when you're not gaming and run directly from the wall outlet when you are. There is a manual switch right on the unit.

(Caveat: the AP019 I have indicates a maximum rating of 12 amps. At 1,400 watts you'd be running right up against 11.7 amps worth of current drawn.)

I'm not aware of too many UPSes that will let you overload them by any appreciable degree before they shut down. (The older CS350/500 models as mentioned previously are a good example of units that will stay on even if heavily overloaded. I believe that to be a lot of the reason why they were recalled.) And as you note, it's definitely not nice to push one right up to its limits. If you wanted your computer to stay up during power failures when you are gaming, I think the smallest suitable UPS APC sells would be the Smart-UPS 2200. While rather expensive if you were to buy one new, a lot of good used examples are free for the asking or very cheap when the batteries conk out.

Getting one of those would give you the advantage of a computer that stays up for hours when it's not being used for gaming purposes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore