Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Buzzing noise when UPS is running off battery?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Buzzing noise when UPS is running off battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
11
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

Buzzing noise when UPS is running off battery?

I have the RS1000 and recently put new batteries in. The positive and negative connections are using the original adaptor, but the link between the batteries that connects them in series is soldered on there as I lost the original cable. I don't know if this has anything to do with the problem, but if necessary I guess I can find a thicker wire and solder it on there.

Now the problem is that when the power goes off and the UPS is on battery, the computer starts buzzing. It's an electrical sort of buzzing. I'm not sure where in the computer it is, but it's definitely from the computer itself, not the UPS.

So I'm thinking that there must be some problem. It's quite a loud buzzing. I'd usually assume that there was a loose wire or something so the electricity supply wasn't proper. But as far as I can see, the wires are fine.

Also, when I was testing the batteries before I connected them all up properly and put them inside the UPS, I made the series connection using a 6mm copper wire. The buzzing still happened then, so I don't think it's the current wire's problem.

What do you think could be causing this? If you have any ideas then I can try and troubleshoot the problem.

Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

It's coming from your computer's power supply - it isn't a fan of the step-approximated sine wave output of the UPS when on battery. Some power supplies do that. Honestly not sure if it would cause a problem, but I've known a couple of people who didn't like it or felt nervous about it, so they connected their computer to a Smart-UPS (pure sine wave) instead.

It's just a matter of how similar the power output is to regular electricity. Normally a sine wave (without distortion) is an even curve, but the UPS you have is more like stair steps following the wave. Check out the pictures from this article - namely the one at the bottom - that might help your understanding.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

I have the RS1000 and recently put new batteries in. The positive and negative connections are using the original adaptor, but the link between the batteries that connects them in series is soldered on there as I lost the original cable. I don't know if this has anything to do with the problem, but if necessary I guess I can find a thicker wire and solder it on there.

Now the problem is that when the power goes off and the UPS is on battery, the computer starts buzzing. It's an electrical sort of buzzing. I'm not sure where in the computer it is, but it's definitely from the computer itself, not the UPS.

So I'm thinking that there must be some problem. It's quite a loud buzzing. I'd usually assume that there was a loose wire or something so the electricity supply wasn't proper. But as far as I can see, the wires are fine.

Also, when I was testing the batteries before I connected them all up properly and put them inside the UPS, I made the series connection using a 6mm copper wire. The buzzing still happened then, so I don't think it's the current wire's problem.

What do you think could be causing this? If you have any ideas then I can try and troubleshoot the problem.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

The battery-to-battery connector is usually where the fuse is. If you replaced a fuse with a solid wire, then the UPS is at risk of battery rupture/fire if the components fail inside especially with the newer plastic cabinet units.

The buzzing sound is due to modified square wave output. It's a normal behavior and it most likely will add moving stripes on a CRT monitor and noise into speakers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

There wasn't a fuse with the old battery to battery connector. It was just a plain wire. I could hook up a fuse it necessary. What amp fuse would it need to be?

What does it mean if the square wave output is modified? What exactly has made it change? So I don't need to worry about it then? There is no speaker noise and I don't have a CRT monitor. I was just worried if it was a problem or not.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

It's coming from your computer's power supply - it isn't a fan of the step-approximated sine wave output of the UPS when on battery. Some power supplies do that. Honestly not sure if it would cause a problem, but I've known a couple of people who didn't like it or felt nervous about it, so they connected their computer to a Smart-UPS (pure sine wave) instead.

It's just a matter of how similar the power output is to regular electricity. Normally a sine wave (without distortion) is an even curve, but the UPS you have is more like stair steps following the wave. Check out the pictures from this article - namely the one at the bottom - that might help your understanding.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
voidstar_apc
Contributor

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

Here's a good [picture of a modified square|http://www.panelectron.hu/webshop/images/square_modified_sinewave.jpg].

I wouldn't worry about the buzzing if the computer and UPS are working normally.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

Thankyou for the picture.

I am also wondering how I can extend the running time of the UPS. I thought it would be better to not start a new thread when I only need one reply here.

In a previous thread I was told that the UPS needs 24v to run properly. Therefore the 2 batteries are wired in series to reach a total of 24v. I was also told that the connector at the back allows for more batteries to be connected to extend the runtime.

If I were to get my hands on another APC connector so I could actually use that connection at the back, how would I wire the battery up? I mean can you only have one battery connected to the back? Or could I have 2 batteries connected in parallel so that I'd have a whole lot more runtime?

Unfortunately all I have available to me are the cheap batteries available where I live in India. The original APC batteries would be very expensive and hard for me to get. These cheap ones don't really last very long even when they are fully charged. So I need to add one or 2 more to extend the runtime. Unlike in the rest of the world where a UPS would only act a little bit as a surge protector and pretty much never as an actual UPS, here the power goes off many times a day. Currently the power is cut for 4 hours a day, that's the best it's been in a long time.

Also, what wattage would the UPS be using when it is charging the batteries? I mean it is a 1 Kilowatt UPS, but it wouldn't use that much to charge the batteries would it? Does anyone know how much it would use?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

a) The BR1000 does not have a connector for extended run batteries, only the BR1500 in the Back-UPS family has that feature. Also, the 1500 model is designed to accept only one battery pack.

b) APC wouldn't be able to offer any instructions for wiring your own battery, though if you're having such poor luck with the cheap batteries you're using, maybe it would be worthwhile to get the more expensive ones? ?:|

c) The charger in the BR1000 is only 20w.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

I have the RS1000. It has a connection at the back. It fits the connector that is used to wire up the main batteries. Does the RS model have this feature?

20w? Wow, must take quite a long time to charge up the batteries fully?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

RS is the family (Back-UPS RS), not the model. If you look on the unit (back or bottom usually), there will be a white sticker with barcodes on it. This will have the exact model and serial number. What do you have?

Yeah, the battery chargers aren't too beefy since, like you said, most of these units' implementations aren't for very frequent or extensive outages.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

Mine says BR1000-IN.

At the back of the UPS where the connector is, it says "BR24BP Battery Pack".
The connector is there and does work when batteries are plugged in. How can I use it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

0 Likes
0
12411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:36 AM . Last Modified: ‎2024-03-22 02:25 AM

Ah, sorry about that. I only really know the North American models well; the BR1000-IN does have that functionality, too.

In terms of using it, well... All I can really tell you is what you already seem to know. It's a 24v battery pack, though it is only designed to have one 24v pack connected, no more than that. Anything beyond that is using it at your own risk, and certainly not APC supported... Maybe someone else has had luck custom-fitting more than one?

Additionally, there are other models that can support more than one battery pack, so you may want to look into those options. Depending on how much capacity you need, you could check out the [SUA750XLI|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SUA750XLI] or [SUA1000XLI|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SUA1000XLI]. Different receptacles than the unit you have now, though I honestly don't know if any of those exact receptacles are available on Smart-UPS models...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore