Beeping and clicking everywhere - 3 of 4 units with same issue at same time

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Beeping and clicking everywhere - 3 of 4 units with same issue at same time
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

0 Likes
3
538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

Beeping and clicking everywhere - 3 of 4 units with same issue at same time

Yesterday my son called me at work and said "the computers are beeping all over the house." My wife called me on the way home an hour later and said "the phones and the Internet connection are down."

When I got home I found that 3 of my 4 APC UPS units (Backups 550 x2, Backups 350 and Backups ES 350) were beeping and clicking like crazy. Only the older Backups ES 350 was not beeping. Looking at the log for one of the computers I saw that the computer thought that AC power was going away and coming back about every second. This was happening on 3 of the four APC UPS units scattered in different rooms in the house. This problem had been going on for over an hour. I asked my wife and son if any of the lights in the house and been flickering or doing anything strange at all and they told me "no." I checked power line voltage and frequency and found them to be fine while the UPS units were still acting up. Batteries in all units were replaced 6 months ago.

My best guess as to what went on was that there was some sort of power line noise or other AC power line anomaly that managed to get the UPS units into a bad state. I suspect a software defect in the UPS units allowed them to stay in this bad state after the initial power line problem was no longer an issue. Even if the power line quality had still been a problem, the cycling back and forth between AC and battery didn't make any sense.

These units had all worked fine for five years before this without any issue. Since this problem I've sent sensitivity from "high" to "medium." I doubt the issue will happen again anytime soon, but I am afraid I've lost confidence in the APC UPS units now. I'm concerned because these units back up telephone, alarm system, Internet, etc. Has anyone ever seen anything like this happen before?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

0 Likes
0
538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

Dirty power, distortion, line noise are not things the UPS can report as it's something the UPS senses with the incoming power. These are unfortunately the smallest, most basic units we make so the info seen is limited. I would recommend contacting tech support to see if there is anything they can do(such as an RMA etc)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

0 Likes
0
538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

When you mention the log, do you mean our software? powerchute personal edition? It is possible the UPS saw some sort of power issue such as line noise, distortion, dirty power etc that could cause this to happen. The ups is capable of seeing these issues without you knowing about it(light flickers etc) Unfortunately, the best course of action is to change the sensitivity(which you have already done) and to monitor and see if it happens again. During this time, were you aware of any power issue/work being on done etc?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

0 Likes
0
538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

This was seen using apcupsd on my server. I looked at the apcupsd source and there is no unique event available to be logged for noise or distortion on the AC input. I have Powerchute installed on a workstation PC, but that PC wasn't turned on at the time. I wasn't aware of any work being done on the power lines. I've had powerline noise before, but it never has lasted for more than a few seconds at a time. All the UPS units were still clicking and beeping when I returned home several hours later.

Apr 17 15:56:27 gator apcupsd[3804]: Power failure.
Apr 17 15:56:28 gator apcupsd[3804]: Power is back. UPS running on mains.
Apr 17 15:56:29 gator apcupsd[3804]: Power failure.
Apr 17 15:56:30 gator apcupsd[3804]: Power is back. UPS running on mains.
Apr 17 15:56:31 gator apcupsd[3804]: Power failure.
Apr 17 15:56:32 gator apcupsd[3804]: Power is back. UPS running on mains.
(above sequence repeats until)
Apr 17 16:10:34 gator apcupsd[3804]: Power failure.
Apr 17 16:10:35 gator apcupsd[3804]: Power is back. UPS running on mains.
Apr 17 16:10:35 gator apcupsd[3804]: Power failure.
Apr 17 16:10:36 gator apcupsd[3804]: Reached remaining time percentage limit on batteries.
Apr 17 16:10:36 gator apcupsd[3804]: Initiating system shutdown!
Apr 17 16:10:36 gator apcupsd[3804]: User logins prohibited
Apr 17 16:10:36 gator wall[9124]: wall: user root broadcasted 1 lines (39 chars)
Apr 17 16:10:36 gator wall[9121]: wall: user root broadcasted 1 lines (69 chars)
Apr 17 16:10:36 gator shutdown[9127]: shutting down for system halt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

0 Likes
0
539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:02 AM . Last Modified: ‎2024-03-21 04:26 AM

Dirty power, distortion, line noise are not things the UPS can report as it's something the UPS senses with the incoming power. These are unfortunately the smallest, most basic units we make so the info seen is limited. I would recommend contacting tech support to see if there is anything they can do(such as an RMA etc)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of