Battery connected NAS loses power on ES 550

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Battery connected NAS loses power on ES 550
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
118
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
7
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Battery connected NAS loses power on ES 550

Hi!

I have a problem with my Back-up UPS ES 550 (BE550-GR / 5B0649U02546). Firmware 828.D2.I
According to PowerChute the remaining battery charge is 100% and estimated performance is 11minutes.

While power outage the NAS or lamp lasts for 0-2seconds and then quits and a constant tone starts. PowerChute still shows 100% or 99% and also notices that it is on battery power. Although my NAS (or whatever equipment) do not receive the battery power.

The problem started about a month or two ago. Last week I replaced the battery, no change.

What should I do?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Good deal!

Thank you for using APC Discussion Forum. Have a great week Janne!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Hi Janne,

I would like share to you this Kbase regarding drop load when connected to a BackUPS unit especially when UPS still up and on battery.

Please let us know if you have further question.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Hi,

and thanks for the reply. Unfortunately none of the problems ably so the only reason left is "Problem #8: The UPS may be faulty". Anything else I could try?

Has anyone got their UPS repaired, is it worth it? Or should I just go the to shop and buy a new one.

What bothers me is that I just bought a new battery because I thought that would be the reason to the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Hi Janne,

If this is an out of warranty unit, I would suggest you to do trade ups so you can take advantage of discount that our company offers. You may go for Smart UPS which is more compatible with almost all loads, such as servers.

Where did you purchase the battery?

I hope you can call our technical support hotline at 800-800-4272 so our rep can better assist you about this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Hi,

Yes, it is out of warranty and was purchased in Finland (www.verkkokauppa.com) and the battery was purchased from the same place. Do you have support in Finland? And I wonder if the battery can be returned?

Is any of the "current" ups compatible with the battery I just bought (eg. APC Back-UPS ES 550VA)?

A great deal of your ups seem to work with ReadyNAS NV+ but I do not know which would be the best one (http://www.readynas.com/forum/viewforum.php?f=88&sid=a54a6d48bb42787cb48032ede3301b70)? What I need is to avoid power failures and have a shutdown process.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Hi Janne,

Yes, we do have a support in Finland. Their sales contact number is +358 10 8374 600. You may always ask them if you can return the battery and you will just do tradeups instead although i'm not certain if they have such deal as that. We have available BackUPS Pro G 550, the part number is BE550G but if you plan to use the NAS on it, im not sure if that is compatible so I would suggest you to tradeup your old unit to a Smart UPS - which is compatible with almost all loads, especially to servers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Thank you for your help. I returned the battery to verkkokauppa.com today and got refunded. I also ordered a new ES 550VA for my NAS as it was listed as compatible on the ReadyNAS forums. I should get it in a couple of days.

Thanks and have a great summer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

0 Likes
0
1183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 AM . Last Modified: ‎2024-03-21 05:36 AM

Good deal!

Thank you for using APC Discussion Forum. Have a great week Janne!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore