BackUPS 700ES

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BackUPS 700ES
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
107
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

0 Likes
4
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

BackUPS 700ES

I'm having a problem with a 3 year old BackUPS 700ES which I have powering my home gateway/router machine (a MiniITX system). For a few months now, whenever I turn it on after being away, as soon as I press the power button on the unit itself, it will start making a whining/squealing noise. It's as if it's trying to make a constant beep but can't quite manage to. If I unplug some of the plugs on the UPS protected strip, it will sort itself out and start working normally. This hasn't been too much of a problem until recently, when it's started doing this entirely at random while the power is on. I've never been next to it when it happens, but it seems that everything on the UPS strip is suddenly powered off, and the UPS starts squealing. Again, this can be sorted out by removing some of the load on the UPS. Could this be as simple as a battery problem, or does it sound more fundamental?

Edit: a bit more information since I wrote the above at work after the UPS had switched itself off, and have just been home to reset it. The serial number is 5B0732U02658, didn't note down the exact model number. While the buzzing beep is going on, the LED is behaving in a similar way, flickering as if it's trying to come fully on. I've read other posts that suggest this might be due to an overload, I doubt this very much as the load is normally < 10%, but just in case I've moved one of the things that was plugged into it onto the non-UPS side. It now has only only an ADSL modem, gigabit switch and MiniITX PC plugged in, and apcupsd is reporting 3% load.

Message was edited by: abayliss

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
  • beeping
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

Also The Ups Can Go Into Overload Often If The Battery Is Bad

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

Have you ever replaced the battery on this unit? The serial number tells us that the unit was manufactured on the 32nd week of 2007. From the way that it behaves, it shows that all of a sudden the unit has detected an overload condition.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

No, it's still using the battery it shipped with. Is an overload when under very low load a symptom of the battery needing replacing? The light on the unit is only ever green, not red (which is what indicates the battery needs replacing isn't it?)

Message was edited by: abayliss

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

With a very low load to no load at all, the UPS shouldn't go into overload unless there's something wrong with the UPS. Typical lifespan of our batteries is 3~6 years depending on the usage and environmental conditions.

Can you send me a PM with the following details:
Complete Name:
Complete Address:
Phone:
E-mail:
Complete Model # of the UPS:

If this is being used for business do include:
Company Name:
Position

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

0 Likes
0
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:07 AM . Last Modified: ‎2024-03-21 05:07 AM

Also The Ups Can Go Into Overload Often If The Battery Is Bad

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore