Back-UPS XS 1300 Not Charging, Not Showing Errors

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS XS 1300 Not Charging, Not Showing Errors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

0 Likes
7
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

Back-UPS XS 1300 Not Charging, Not Showing Errors

My Back-UPS XS 1300 (BX1300LCD) appears to be fine (no error messages, no indicators on, no beeping), but it is showing 0/5 bars of battery left and 0 minutes of run time. Since it is about 3 years old, I figured the batteries need replaced, so I got a new set of APC RBC109 replacements. When I first put the batteries in, the battery meter showed 3/5 bars and a positive number for run time. After leaving it to charge up to full, it showed 0/5 bars and 0 minutes again.

I noticed the new batteries tested at 24v+ when I installed them, but now test at 21.4v. It appears the UPS is draining them instead of charging. Power Chute shows the batteries are charging with 0% available. Self test using the buttons on the front shows nothing. Power Chute claims it is unable to perform a self test. The UPS display shows 124v input at 60.0Hz.

I haven't been able to find my receipt yet, so I'm not sure if it's still in warranty (right at the edge if it is, since it was made in 12/07).

This problem seems very much like this similar unanswered thread:

Referenced content removed

Any help would be greatly appreciated.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • bx1300lcd
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:04 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:04 PM

in this case it is an eeprom fault,i advice you to take your unit to an apc authorised service center, and you can contact apc custumer care center.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 7
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

Yeah that unit needs to be service already.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

Yes, this is the first time I've replaced the battery in this unit. Using Power Chute to 'Replace Battery Date' had an interesting affect. The battery meter on the LCD went to 5/5 bars and showed 100% in PC, and run time was showing 800+ minutes (no load). After a minute or two, it started dropping. I let it go to see if it was trying to calibrate itself. After a hour or two, it was back down to 0/5 bars and 0 run time (0% in PC as well). I tested the battery and it is still at 21.4v.

I also tried removing the battery and pressing 'Replace Battery Date' and it did the same thing! It never complained about not having a battery. It just showed 100%, then slowly started dropping again.

I also tried pulling the power (after the 'Replace Battery Date') with a small (7W) load on it. With the new battery, it stayed on for 1 second. Without a battery, it went off immediately. With the old battery, it also went off immediately.

Self test in PC still shows 'Unable to carry out a self-test at this time' no matter what configuration the UPS is in.

As for attempting to calibrate it, doesn't it have to be able to stay on with a load for a while in order to do that?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

I found my receipt. It's dated 2/20/2008. So in the time I took to diagnose the problem (which started in January), my warranty expired. ๐Ÿ˜ž I'll try calling APC and see if they can help or if I'm screwed.

The Trade-UPS program seems to be a joke. If I trade in the unit on a new 1500, I can pay a lot more than they are new on Amazon.

Does anyone know if I can do anything to the EEPROM myself (reprogram, replace, etc.)?

Thanks for all the help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

before you calibrate the battery you need to set the date replaced of the battery then you do the calibration mode,if this procidure not help full try to check the eeprom of the unit through a hyper terminal program.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

Is this your first battery change since you bought the unit? If yes, u may need to use the Powerchute to tell the unit that you have installed a new battery.. Connect the usb cable that came with your unit, unit should be on, use the powerchute and try to look for the "new battery"(forgot the exact term or words used). You should see it there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:05 PM

Try to calibrate the unit when the battery shows full charge, during calibration load must be stable and do not exceed 20% of ups load capacity.
and you have to change the date time for last battery replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:04 PM

0 Likes
0
1891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 05:32 AM . Last Modified: โ€Ž2024-03-21 11:04 PM

in this case it is an eeprom fault,i advice you to take your unit to an apc authorised service center, and you can contact apc custumer care center.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of