Back-UPS XS 1200 battery connection question

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS XS 1200 battery connection question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:02 AM

0 Likes
7
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:02 AM

Back-UPS XS 1200 battery connection question

Hi,

I'm trying to use a Back-UPS XS 1200 that was purchased about 2 years ago, but is just now being used for the first time - it's been sitting in the box for all that time (PowerChute indicates the last battery replacement was June 8, 2006).

When I turn on the UPS, the "replace battery" light flashes, but the PowerChute software keeps flipping back and forth between reporting "Battery in APC unit is disconnected", and "Your battery backup is operating normally". It switches every few seconds.

From what I've read, it sounds like I should expect to have to purchase a new battery based on the amount of time that the unit sat unused. The messages from PowerChute are confusing me, though - are they consistent with a dead battery, or do they indicate that something might be wrong with the connection to the battery? I've tried disconnecting and reconnecting the battery several times, with no change in the results.

It's not a problem for me to purchase a new battery, but I'm just trying to avoid wasting money in case the problem is with the connection cables rather than with the battery itself. Any help would be appreciated!

Thanks,
Ryan.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 3_years
  • repair
  • rma
  • warranty
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

0 Likes
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

rau wrote:
You should never let lead acid batteries sit for more then a year withou being charged. They lose charge naturally and when it reaches a point of very low charge, it enters in a "self destroying" state. Lead acid battery when are deep discharged it's plates start to oxidize.
Yep, that'd be a good advise for future, however in his case, I'd still make a warranty claim.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:02 AM

0 Likes
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:02 AM

Hi Notorious,

I have tried disconnecting and reconnecting the battery several times, but it never gets rid of the problem. The connection seems secure, and there only appears to be one way to connect the plugs, so I'm pretty sure I'm doing it correctly. The Replace Battery light is always flashing, though.

The software reports an intermittent connection - for a couple of seconds it will say the battery is connected properly, then it will report no connection. Sounds to me like something is flakey with the connection to the battery.

Are there any other diagnostics I can run myself to figure out the cause of the problem?

Thanks,
Ryan.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:02 AM

0 Likes
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:02 AM

Ryan,

The flashing Replace Battery LED indicates that the UPS is not sensing a battery connected at all. Have you verifed the battery connection (you may have, but we always want to double check)? If so, and the battery is secured properly, then the problem may be the unit itself. The fact that the replace battery is not solid means that the UPS is incapable of sensing a battery present, even if there was an insufficient charge or capacity present on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

0 Likes
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

Unfortunately there aren't. The flashing replace battery with a battery securely connected, regardless of charge, indicates a fault present with the UPS. Since there is only one other user-replaceable part outside of the UPS, being the battery, I can't advise a replacement battery is going to rectify the situation.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

0 Likes
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

just one quick thing i thought of..

if you have the battery connected, with the replace battery LED flashing and plug something into the battery back up outlets (maybe like a lamp or something), does the UPS actually go to battery and support the item or turn off immediately?

if the items stays on, that would mean its only cosmetic, but just as noted above, it is going to be an issue with the UPS that you arent going to be able to solve, whether it works when you pull the plug or not. if it doesnt work then yeah, definitely a problem that you'd need to most likely need to replace the unit or the battery if it happened to be really old. you could always check voltage on the battery itself with a voltmeter.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

0 Likes
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

Call support and make a warranty claim and make 'em fix it under warranty. As far as I know, the 3 year warranty on APC UPSs is "bumper to bumper"
http://www.apc.com/support/service/in_warranty_service.cfm

Check your serial number. It would be something like AB0612##### which indicates the UPS was built in the 12th week of 2006. If the serial # is within 3 years of when you make the claim or you have a receipt that's dated within 3 years of when you call , your claim should go through.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

0 Likes
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

You should never let lead acid batteries sit for more then a year withou being charged. They lose charge naturally and when it reaches a point of very low charge, it enters in a "self destroying" state. Lead acid battery when are deep discharged it's plates start to oxidize.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

0 Likes
0
1242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:38 PM . Last Modified: ‎2024-03-26 12:01 AM

rau wrote:
You should never let lead acid batteries sit for more then a year withou being charged. They lose charge naturally and when it reaches a point of very low charge, it enters in a "self destroying" state. Lead acid battery when are deep discharged it's plates start to oxidize.
Yep, that'd be a good advise for future, however in his case, I'd still make a warranty claim.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of