Back-UPS Pro 1500 (BR1500G) won't power on without battery attached

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS Pro 1500 (BR1500G) won't power on without battery attached
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

0 Likes
3
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

Back-UPS Pro 1500 (BR1500G) won't power on without battery attached

I have a BR1500G that stopped functioning properly after a battery replacement (genuine APC replacement battery).  I made a post a while back about the primary symptom (battery will charge, but not stay charged), but I've realized that a major symptom is that the unit will not power on without a battery attached.  All other 1500G units will turn on without the battery attached and this one no longer will.

Any idea what internal failure might have caused this?  I'm interested in trying to repair it if possible.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

Unfortunately I have mixed feelings with this series, I have 3  ( all with the external battery pack) and 2 of them have problems where one of them started when brand  new , requiring a brain dead reset every time it was plugged ( I forwarded this UPS  to a relative in South America so I couldn't send it back to honor the  warranty ) and since then every time there is a blackout and it exhaust it's battery and turn itself off, when the power return it has to be reset through the brain dead procedure so a unattended installation is out of question.    The second one after a couple of years started to show always a maximum of 330 remaining minutes without any load. Batteries were replaced ( both internal and on the external battery pack) and followed the APC recommended procedure to reset the remaining time allowing it to discharge with a 50% load without any success.  By the way opening the external battery pack to replace it's 4 internal batteries is a nightmare when the housing of this batteries got deformed and inflated which jammed  the external battery pack sliding side panel and had to broke part of it. 

Our newer UPS  are the  SMT and SMX  series, all equipped with network cards and managed remotely 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

Have you tried to Brain Dead it ?     Unplugged, no battery and pushing, without releasing it,  the power button for 30 sec ? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

Thank you for the suggestion.  I had tried a bunch of "resets" when this first happened (battery out, unplugged, hold down power button for 10 seconds and then insert battery), but not a "braid dead" reset of 30 seconds.  I just tried that and there was no change.  I really think that this is a hardware issue where the 24VDC power supply is dead, but the DC battery charging circuit works.  The unit will still charge the batteries, but won't keep them charged and won't work without a battery plugged in.  It's as if the batteries are being used for the DC internal DC supply voltage since the one inside the unit is dead.

Reply

Link copied. Please paste this link to share this article on your social media post.

robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

0 Likes
0
2383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 PM . Last Modified: ‎2024-03-26 02:49 AM

Unfortunately I have mixed feelings with this series, I have 3  ( all with the external battery pack) and 2 of them have problems where one of them started when brand  new , requiring a brain dead reset every time it was plugged ( I forwarded this UPS  to a relative in South America so I couldn't send it back to honor the  warranty ) and since then every time there is a blackout and it exhaust it's battery and turn itself off, when the power return it has to be reset through the brain dead procedure so a unattended installation is out of question.    The second one after a couple of years started to show always a maximum of 330 remaining minutes without any load. Batteries were replaced ( both internal and on the external battery pack) and followed the APC recommended procedure to reset the remaining time allowing it to discharge with a 50% load without any success.  By the way opening the external battery pack to replace it's 4 internal batteries is a nightmare when the housing of this batteries got deformed and inflated which jammed  the external battery pack sliding side panel and had to broke part of it. 

Our newer UPS  are the  SMT and SMX  series, all equipped with network cards and managed remotely 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now