Back-UPS Pro 1000 Replace battery flashing but Battery Charge indicator full

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS Pro 1000 Replace battery flashing but Battery Charge indicator full
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
117
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

0 Likes
4
10452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

Back-UPS Pro 1000 Replace battery flashing but Battery Charge indicator full

The UPS was beeping saying we needed to replace the battery, so we did. We purchased a NEW battery specific to the UPS. We installed the battery. Now, please see below.

As the topic says, the UPS is giving us a blinking battery image with an X in the middle of it. The blinking "x-battery" is right next to the Battery Charge bar. The bar is full and shows to be fully charged. 

Again, this battery is brand new.

There are no other indicators showing up other than "on line". (the plug). The "load" is at 14%, we don't have much plugged into it.

I am not able to easily reset this UPS due to it powering a network switch.

Why is the replace battery blinking of the battery is brand new and the Batter Charge bar is completely full?

Thank you for your help.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 1000
  • apc
  • back-ups
  • battery
  • replace
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

0 Likes
0
10446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

Hi,

On 2/2/2016 9:16 AM, David said:

I'll give this a try next time I can. Quick question, does running a self-test cause any power issues? In other words, can I do this while it's plugged in an fully operational or is it going to shut itself off during the self-test?

The UPS run a self-test every 2 week and at start up while in operation. So running a self-test should not cause a shut down of attached equipment. If you are concerned I recommend waiting until there is a time when the load can be powered down and then run the test. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

0 Likes
0
10445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

Hi,

Let the new battery charge for 12 hours run and then run a self-test. If the issue is not cleared after the self-test then you should reset / brain Dead the UPS.

Reset / Brain Dead

1: Disconnect any attached load.

2: Unplug the UPS from the wall socket.

3: Disconnect the UPS' internal battery.

4: Push and hold the "On" button on the UPS for 5 seconds

5: Reconnect internal battery.

6: Plug UPS in to known good power source.

7: Turn UPS on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

0 Likes
0
10445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

Thank you Bill for the reply.

I'll give this a try next time I can. Quick question, does running a self-test cause any power issues? In other words, can I do this while it's plugged in an fully operational or is it going to shut itself off during the self-test?

Also, side note: the UPS has been plugged in for over a week.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

0 Likes
0
10447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

Hi,

On 2/2/2016 9:16 AM, David said:

I'll give this a try next time I can. Quick question, does running a self-test cause any power issues? In other words, can I do this while it's plugged in an fully operational or is it going to shut itself off during the self-test?

The UPS run a self-test every 2 week and at start up while in operation. So running a self-test should not cause a shut down of attached equipment. If you are concerned I recommend waiting until there is a time when the load can be powered down and then run the test. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

0 Likes
0
10445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:13 AM . Last Modified: ‎2024-03-27 01:55 AM

I had exactly the same problem, and I confirm that Bill's procedure works.  Thanks.

  • Tags:
  • battery
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore