Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back-UPS ES 725 No Data Port?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS ES 725 No Data Port?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:20 AM

0 Likes
6
2163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:20 AM

Back-UPS ES 725 No Data Port?

I have been Googling this issue for days and can't find any information.

I have two Back-UPS ES 725's in the office and for some reason the power supply here is messed up and they like to beep randomly - maybe every 5 minutes, maybe once a week - depending on something I don't know.

I wanted to install the PowerChute software to disable the beeping but the data port had a plastic cover over it. I popped it off and was able to plug my RJ45 - USB cable in but the computer does not recognize it.

Is this data port disabled or something? Is there nothing I can do other than call an electrician or buy a new Back-UPS?

Thanks in advance for your help.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 02:58 AM . Last Modified: ‎2024-03-22 02:19 AM

0 Likes
0
2163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:58 AM . Last Modified: ‎2024-03-22 02:19 AM

What is the exact Model number of the UPS? Is it DL725VT or BE725BB? You can find the UPS model number on a white bar code sticker at the rear of the unit.

fyi..the DL725VT does not have the data port.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:20 AM

0 Likes
0
2163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:20 AM

I have been Googling this issue for days and can't find any information.

I have two Back-UPS ES 725's in the office and for some reason the power supply here is messed up and they like to beep randomly - maybe every 5 minutes, maybe once a week - depending on something I don't know.

I wanted to install the PowerChute software to disable the beeping but the data port had a plastic cover over it. I popped it off and was able to plug my RJ45 - USB cable in but the computer does not recognize it.

Is this data port disabled or something? Is there nothing I can do other than call an electrician or buy a new Back-UPS?

Thanks in advance for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:20 AM

0 Likes
0
2162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:20 AM

It doesn't actually say "Data Port" on the port, as seen in the manual...which leads me to believe this is disabled for some reason.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:20 AM

0 Likes
0
2163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:20 AM

I've never heard of the data port having a cover on it. Is it labeled "data port?" Maybe a picture would help? I know that style cable isn't too common so I'm assuming it's the one that came with the UPS... but it's always good to double check.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:19 AM

0 Likes
0
2163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:19 AM

It is in the same spot as the data port in this image from APC website:
http://www.apcc.com/products/moreimages.cfm?partnum=BE725BB&aPos=2

I almost didn't think it was there because the plastic cover is the same color as the unit and was not too easy to pry off.

I am not at the office until Monday to check if it actually says Data Port or not but it's in the same spot as the one in the picture and fits perfectly with the RJ-45 cable.

I am indeed using the cable that came with the unit - I have never seen another cable or a purpose for RJ-45 to USB.

Thanks for the help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:19 AM

0 Likes
0
2163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:57 AM . Last Modified: ‎2024-03-22 02:19 AM

And it's the same case with both 725s? Do you know where you purchased them? As far as I know they weren't disabled...

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 02:58 AM . Last Modified: ‎2024-03-22 02:19 AM

0 Likes
0
2164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:58 AM . Last Modified: ‎2024-03-22 02:19 AM

What is the exact Model number of the UPS? Is it DL725VT or BE725BB? You can find the UPS model number on a white bar code sticker at the rear of the unit.

fyi..the DL725VT does not have the data port.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore