Back-UPS ES 700 strange alarm behaviour

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS ES 700 strange alarm behaviour
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
maxpower
Crewman maxpower
Crewman

Posted: ‎2022-07-05 01:19 PM . Last Modified: ‎2022-07-14 10:29 AM

0 Likes
1
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-05 01:19 PM . Last Modified: ‎2022-07-14 10:29 AM

Back-UPS ES 700 strange alarm behaviour

Device: Back UPS ES 700

connected device: just one router, nothing more. for testing purposes: a lamp

 

When I pull the plug for test purposes, the ES 700 makes a very annoying high pitched terribly loud sound. Calling it a "beep" would be understatement.

 

It stops when I disconnect the consumer. While the ES 700 beeps the LED on the device is very low.

 

When doing the same test without any consumer connected, just the ES 700 and now pull the main´s plug, this sound does not occur.

 

The ES 700 does not tell to replace the battery. Though, the battery is aging and need replaced, i  know.

 

I just wonder whether to get a new battery or better retire the whole UPS. I dont want to waste the money for a new battery.

 

Thanks

 

EDIT: according to some Yt people with similar symptoms, this may be due to defective MOSFETs.

I´ll see if I find someone to repair. Though being old, I´m reluctant to throw away such pricy piece of hardware....

 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-08-25 07:37 PM

0 Likes
0
526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-25 07:37 PM

Hi @maxpower 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the late revert, though there is a possibility that the UPS had an internal failure, it would also help if you can provide the exact model of the UPS for us to confirm the state that the UPS is in.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of