Back-UPS ES 700 momentary power outage

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS ES 700 momentary power outage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:49 AM

0 Likes
3
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:49 AM

Back-UPS ES 700 momentary power outage

Hello,

our company uses three APC Backup-UPS ES 700 (700 VA / 405 W) units and we are experiencing some strange power outages on two of them. Let me describe the setup:

Unit #1:
- 2 PCs (with G620 and G840 processors) in the BATTERY sockets
- 2 screens in the BATTERY sockets
- 1 desk phone in the SURGE socket
- 1 HP 3010 printer in the SURGE socket

Unit #2:
- 2 PCs (with G620 and i5-530 processors) in the BATTERY sockets
- 2 screens in the BATTERY sockets
- 1 desk phone in the SURGE socket
- 1 nondescript old audio speaker in the SURGE socket

Unit #3:
- 1 PC (with the Athlon 64 X2 4200+ CPU) in the BATTERY socket
- 1 screen in the BATTERY socket

Each of the units is plugged straight into the wall. Units #2 and #3 are in the same room and (obviously) plugged into different wall sockets. Yes, I checked, the batteries are present, and according to powerchute, the offending unit #1 that I'm checking right now has 83 % of battery charge. Please note that #1 is several years old (the APC logo is in fact still red, I presume these are a more dated version), but #2 is only several months old. Battery replacement has been done regularly.

Now on to describe the problem:
The affected units are #1 and #2. The PCs are normally working, then, suddenly, the UPS beeps ONCE, the connected devices power cycle, and everything goes back to normal. Happens irregularly, however the highest frequency (and the point where I finally found it strange) was twice in one week.

Is there any battery or UPS - related reason for this? The single beep leads me into thinking that something is causing the UPS to restart. Is there some problem with the UPS or battery, or does it simply mean that we are overloading the units or that our electrical network is just bad?

I would be thankful for any help. Cheers.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • beep
  • problem
  • question
  • shutdown
  • ups
  • windows
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:48 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:48 AM

On 2/27/2017 4:14 PM, Merick said:

Can you provide the model number and serial number of the unit which is located on the bottom of the unit (on a white barcode sticker).

Hello, the numbers are as following:

Unit #1:
BE 700-CP
5B0945T78017

Unit #2:
BE 700G-FR
5B1617T47196

On 2/27/2017 4:12 PM, Secret Squirrel said:

I would then add two additional UPS, to lighten the load being carried between UPS#1 and UPS#2.

We might do this as a last resort. I forgot to mention - yesterday, me and my boss were hooked to unit #2. That is two monitors, two PCs in the battery slot (with G3240 and i5-6400 CPUs - so no lightweights) and nothing ill happened. However, as I was checking unit #1 with nothing except for data cable plugged in, I heard it switch to battery two times during ~3 hours, always only for a few seconds.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:49 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:49 AM

Hello Jan,

If the units were being Overloaded, you would receive a Constant Tone from the UPS when switching to battery power and witness the load powering off. This does not appear to be the symptom you've described.

In your configurations however, the load does appear to be significant. With large loads, we may experience diminished run-times when transferring to battery. The more discharges and recharges that the internal batteries experience, the weaker they will become over time. Eventually the batteries will no longer be able to support the connected load.

Based on your description, it appears the units may be attempting to temporarily switch to battery power and are finding that upon switching, they are unable to support the load.

The HP 3010 printer you've indicating as being plugged into the Surge Only outlet of 1st unit may have something to do with the issue. Laser printers are continuously active when powered on and will often "sag" an electrical circuit. This "sag" can cause electrical disturbance which force the UPS to battery, more frequently than is normally expected. This can prematurely weaken the batteries. 

I would recommend attempting to electrically isolate the Laser Printer, preferably it's own dedicated electric circuit. I would then add two additional UPS, to lighten the load being carried between UPS#1 and UPS#2.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:48 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:48 AM

Hi Jan,

Can you provide the model number and serial number of the unit which is located on the bottom of the unit (on a white barcode sticker).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:48 AM

0 Likes
0
1231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:40 AM . Last Modified: ‎2024-03-27 12:48 AM

On 2/27/2017 4:14 PM, Merick said:

Can you provide the model number and serial number of the unit which is located on the bottom of the unit (on a white barcode sticker).

Hello, the numbers are as following:

Unit #1:
BE 700-CP
5B0945T78017

Unit #2:
BE 700G-FR
5B1617T47196

On 2/27/2017 4:12 PM, Secret Squirrel said:

I would then add two additional UPS, to lighten the load being carried between UPS#1 and UPS#2.

We might do this as a last resort. I forgot to mention - yesterday, me and my boss were hooked to unit #2. That is two monitors, two PCs in the battery slot (with G3240 and i5-6400 CPUs - so no lightweights) and nothing ill happened. However, as I was checking unit #1 with nothing except for data cable plugged in, I heard it switch to battery two times during ~3 hours, always only for a few seconds.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore