Back-UPS ES 550 - Red Light Flashes and Continuous Beep

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS ES 550 - Red Light Flashes and Continuous Beep
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
8
21488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-26 10:46 PM

Back-UPS ES 550 - Red Light Flashes and Continuous Beep

My UPS has been shutting itself down over the past few days. I assumed that this was related to a surge or something. Now, when I turn it on, the red light flashes and the unit makes a continuous tone. When I checked PowerChute yesterday, it said the battery was at 67%.

Does anyone know what this means? Model: BE550G-CN.

Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

See if your situation is covered by this KB article:

http://www.apc.com/us/en/faqs/FA158810/

Post back with your results.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

Larry,

Since I posted this, the UPS has been steady. However, yesterday when I got home from work, I tried to power on my PC but the UPS had turned itself off some reason. I turned it back on and it was fine. Today, I was on the PC when the UPS started making that continuous beep. I got a PowerChute popup message that said the battery was disconnected (see attached). I quickly checked the battery level in PowerChute and it was at 86%. I shut down and then checked the UPS battery. Both jumper cables were tightly connected to the battery terminals. I really had to pull to get one off. I can't see how this is the problem.

I plugged everything back in and turned on the UPS. It chirps once but the red light flashes. I turn on the PC (which is plugged into a backup/surge outlet). After about 5 or 10 seconds it starts beeping continuously. One thing I have noticed is that if I turn off and on the UPS, but don't turn on my PC, the UPS just flashes red. It's when I turn on the PC that it beeps continuously.

Any ideas what could be happening here?

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

Time to go back to basics and ask questions.

When did you purchase the UPS?  Check the serial number if you are uncertain; the format is leading number, alpha, two digits (which indicate the year of manufacture).

What OS are you running?

What version of PowerChute are you running on that OS?

And finally, did you follow the instructions in the provided KB article?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

S/N: 3B1033X50761. Can't remember when I bought it.

Windows 10

PowerChute 3.0.2

I did read that KB article an followed the steps but I'm not sure what I learned from it. I seemed to have reset the unit but the problem persists.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

I just ran the warranty check based on your serial number.

Your APC Back-UPS 550VA, 8 outlet, 120V Canada (BE550G-CN) comes standard with a 3 years repair or replace factory warranty. The warranty is effective from the date of purchase. In the event that you are not able to locate a dated proof of purchase receipt, your warranty is effective from the product's manufacture date. Your product was manufactured on August 12, 2010.

This device is clearly past the 5 to 7 year life span of a desktop UPS.  My suggestion is that you use the APC TradeUPS program (Canada/English link: http://www.apc.com/shop/tradeups/ca/en/tradeups/overview.jsp) and get yourself a new one...

The APC Trade-UPS Program gives you:
  • Up to a 25% discount on new APC UPS(s)
    The APC Trade-UPS program* is a cost-effective way to upgrade your existing units and protect your latest investment. Trade in any UPS, regardless of its manufacturer or its working condition, for the latest APC UPS technology and receive up to a 25% discount on your new purchase.*** The Trade-UPS program is currently available in the United States, Canada, Ireland, United Kingdom, France, Spain, Portugal, Austria, Belgium, Czech Republic, Germany, Denmark, Finland, Italy, Luxembourg, Netherlands, Norway, Poland, and Sweden.** This program is applicable for original equipment owners only.
  • Up to a 25% discount on APC accessories
    As a benefit to our customers, now you can also buy additional APC accessories at a significant discount, if purchased along with your Trade-UPS.
  • Upgrade to four times the VA of your current UPS capacity
    Trade in up to 4X the VA of your current UPS capacity or trade in two UPSs for one larger unit.
  • Up to a 3 year factory warranty on new units
  • Free removal and/or shipping of existing units
    Order new units today and receive free return shipping of your retired units back to APC. APC will also pay to have larger UPSs picked up and returned.* *Applicable only to defined easy access areas
  • Proper ecological disposal of returned UPSs and batteries for free
    All old units, including hazardous UPS batteries, returned to APC will then be properly and ecologically disposed of according to Environmental Protection Agency standards (a $5 to $500 value depending on the UPS).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

See if your situation is covered by this KB article:

http://www.apc.com/us/en/faqs/FA158810/

Post back with your results.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

Larry,

Since I posted this, the UPS has been steady. However, yesterday when I got home from work, I tried to power on my PC but the UPS had turned itself off some reason. I turned it back on and it was fine. Today, I was on the PC when the UPS started making that continuous beep. I got a PowerChute popup message that said the battery was disconnected (see attached). I quickly checked the battery level in PowerChute and it was at 86%. I shut down and then checked the UPS battery. Both jumper cables were tightly connected to the battery terminals. I really had to pull to get one off. I can't see how this is the problem.

I plugged everything back in and turned on the UPS. It chirps once but the red light flashes. I turn on the PC (which is plugged into a backup/surge outlet). After about 5 or 10 seconds it starts beeping continuously. One thing I have noticed is that if I turn off and on the UPS, but don't turn on my PC, the UPS just flashes red. It's when I turn on the PC that it beeps continuously.

Any ideas what could be happening here?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

Time to go back to basics and ask questions.

When did you purchase the UPS?  Check the serial number if you are uncertain; the format is leading number, alpha, two digits (which indicate the year of manufacture).

What OS are you running?

What version of PowerChute are you running on that OS?

And finally, did you follow the instructions in the provided KB article?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

S/N: 3B1033X50761. Can't remember when I bought it.

Windows 10

PowerChute 3.0.2

I did read that KB article an followed the steps but I'm not sure what I learned from it. I seemed to have reset the unit but the problem persists.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

Here is what PowerChute says now.

Also, I should point out that I always turn off my PC when I'm not using it and it's the only device plugged into the battery/surge outlets. In an HP ENVY all-in-one. All that's connected to the other outlets are an iPhone adapter, a cable TV receiver and a SlingBox.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

I just ran the warranty check based on your serial number.

Your APC Back-UPS 550VA, 8 outlet, 120V Canada (BE550G-CN) comes standard with a 3 years repair or replace factory warranty. The warranty is effective from the date of purchase. In the event that you are not able to locate a dated proof of purchase receipt, your warranty is effective from the product's manufacture date. Your product was manufactured on August 12, 2010.

This device is clearly past the 5 to 7 year life span of a desktop UPS.  My suggestion is that you use the APC TradeUPS program (Canada/English link: http://www.apc.com/shop/tradeups/ca/en/tradeups/overview.jsp) and get yourself a new one...

The APC Trade-UPS Program gives you:
  • Up to a 25% discount on new APC UPS(s)
    The APC Trade-UPS program* is a cost-effective way to upgrade your existing units and protect your latest investment. Trade in any UPS, regardless of its manufacturer or its working condition, for the latest APC UPS technology and receive up to a 25% discount on your new purchase.*** The Trade-UPS program is currently available in the United States, Canada, Ireland, United Kingdom, France, Spain, Portugal, Austria, Belgium, Czech Republic, Germany, Denmark, Finland, Italy, Luxembourg, Netherlands, Norway, Poland, and Sweden.** This program is applicable for original equipment owners only.
  • Up to a 25% discount on APC accessories
    As a benefit to our customers, now you can also buy additional APC accessories at a significant discount, if purchased along with your Trade-UPS.
  • Upgrade to four times the VA of your current UPS capacity
    Trade in up to 4X the VA of your current UPS capacity or trade in two UPSs for one larger unit.
  • Up to a 3 year factory warranty on new units
  • Free removal and/or shipping of existing units
    Order new units today and receive free return shipping of your retired units back to APC. APC will also pay to have larger UPSs picked up and returned.* *Applicable only to defined easy access areas
  • Proper ecological disposal of returned UPSs and batteries for free
    All old units, including hazardous UPS batteries, returned to APC will then be properly and ecologically disposed of according to Environmental Protection Agency standards (a $5 to $500 value depending on the UPS).
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

OK, I guess mine is due for replacement. I was thinking of the BE600M1 or BN650M1. Do you think that's what I need? All I have connected is my all-in-one desktop and I just want to be able to wrap up and shut down in event of power failure when working.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

0 Likes
0
21466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-26 10:46 PM

While the specs are slightly different, they are - for your purposes - equivalent.

The former is available through the APC TradeUPS program.  The latter is a retail-only model (Staples, Office Depot, Best Buy). Staples, at least, should let you drop off the old unit for recycling.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore