Back-UPS ES 450/550G "off", then flashing red/green

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS ES 450/550G "off", then flashing red/green
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

0 Likes
5
19434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

Back-UPS ES 450/550G "off", then flashing red/green

Ups is powering a PC and security system dvr. Got home and saw PC and dvr were off. Checked ups and saw it was also off. I pressed power button on ups and the ups beeped once and its led is flashing red and green. 

Any idea why the unit would be off? I don't think there was an outage. I have a coffee maker that would've been flashing if so. I had only been away from home for an hour. Would a weak or nearly dead battery cause the ups to turn off even when getting adequate power from the wall? Will the ups no longer stay "on" and forward wall power to connected devices if the battery is low or nearly dead? 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery
  • flash
  • green
  • led
  • red
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

0 Likes
0
19420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

Hello 

I have a Back-UPS ES 550, with serial number 4B1106P16045.  I bought it used and wondered if you can tell me if the battery is still good, and if not, how to order a replacement.  Thank you.

Joanie

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

0 Likes
0
19420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

Hi J,

To clarify one thing, both the BE450G and the BE550G have two sides - a battery backup (+surge) and a surge only side. The surge only side is unaffected by the power on button, if the battery is dead, etc. I'm assuming your PC and DVR were plugged into the battery backup side.

A few things come to mind -

What's the serial number of the UPS and the serial number of the battery (if you have replaced it)? I'm assuming you have either a BE450G or BE550G correct?

Has this UPS been working fine for a while or is this a new install? Has the UPS supported your devices in an outage before?

I have both the BE450G and the BE550G in our lab, and they both will turn on without a battery present. They will however give you a constant tone and flash the red LED, but the UPS itself will pass power on the battery backup side of things.

A scenario that might explain your situation: if the UPS was running a self test (it does so every two weeks) or if there was dirty power (enough for the UPS not to like it but still keeping the coffee maker on), the UPS will go to battery and if the battery was bad, it would drop the load. The LED will flash between greed/red and give a constant tone when a bad battery is present. 

Let me know what you think.

- Tommy

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

0 Likes
0
19420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

Thanks for relying!

It's an ES 450. I've only had it installed for a week. I bought it from an individual. It was used but looked new, but not sure of its actual history. The serial # is 3B1125X13127. It does have a genuine APC battery installed. The negative wire was unconnected when I opened the box last week when I received it. It looked new, with all the accessories and paperwork in place. This UPS replaced a Back-up Network 40 that had been working perfectly (no issues) in the same setup for many months. I needed to move the Network 40 to another room for another purpose.Last night was the first time I had powered on the PC that had been connected to the ES 450 (and that had been working fine for months powered by the on the Network 40). The security system DVR had been plugged up to the ES450 for the last week. The PC had been running fine as I used it for several hours last night (it rebooted several times, which was necessary as I was reinstalling windows). I left home for an hour or two with the PC at idle and came home to find the PC and ES450 powered off. No lights. No beeps. The coffee maker I referred to is plugged into the wall (not into UPS). If its clock is flashing, I know I've had a power outage. It was not flashing when I arrived home this morning. The PC is plugged into the battery side of the UPS's outlets. The PC is my plex video server, so I want it to run 24/7 even in the case of a short power outage. The PC is set to power back on if it loses power and plex then starts itself. This morning, the led on the ES450 was flashing red/green when I turned it back on. It has now flashed those colors for about 7 hours. To test it, I just unplugged it and it simply shut off. No lights or beeps that I recall. When I powered it back up, it was flashing red (actually looks amber). It flashed amber when I received it and while the battery was disconnected. So, today, I opened it up, unplugged battery, measured 13 volts DC across the battery terminal, reinstalled and plugged it back up and again it still flashed red (or amber). Nothing was plugged up at the time. I then plugged the PC into the ES450 and the led turned green and I the powered up the PC with no problems. This is all so confusing!!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

0 Likes
0
19420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

Your Back-UPS ES 450 dates from the 25th week of 2011. If the battery is original, it is either worn out or has been left discharged too long for the UPS to bring it back up. A genuine APC battery should have a serial number of its own.

The UPS is designed to detect power failures and disturbances that some other things (like your coffee maker) may never notice.

A new battery would have your Back-UPS ES 450 up and working like new once again. You could also trade it in for a discount on a newer model with the APC Trade-UPS program, if you would rather have a new UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

0 Likes
0
19421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:03 AM . Last Modified: ‎2024-03-27 01:16 AM

Hello 

I have a Back-UPS ES 550, with serial number 4B1106P16045.  I bought it used and wondered if you can tell me if the battery is still good, and if not, how to order a replacement.  Thank you.

Joanie

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:04 AM . Last Modified: ‎2024-03-27 01:16 AM

0 Likes
0
19420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:04 AM . Last Modified: ‎2024-03-27 01:16 AM

Hi,

When you plug the unit in and power it up it will run a self-test. The test is to determine if the battery is good. Based on the serial number the unit is 7 and 1/2 years old. If the battery has never been replace you should replace it as the expected life is 3 to 6 years. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore