BX1500LCD Dead after power outage.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX1500LCD Dead after power outage.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

0 Likes
3
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

BX1500LCD Dead after power outage.

I have an older BX1500LCD model.


The unit needed a battery, but before I got the chance to order one the power went out, and my unit is now DEAD.

I left the unit in place without the battery as protection against surges. The local utility had an issue where we lost power on one phase (the one where the UPS is on of course) It was a burnt connection in the street that affected 12 houses. Ever since that the unit will not even power up. (Better the UPS than my computer, good sacrifice).

Upon investigation, and poor cash flow, I opened up the unit. Capacitor 69 was slightly bulged so it was replaced with no success. (22 uf 400V) Physically everything looks OK on the board. I do have line in power to the board but nothing to the transformer. (Circuit breaker is good). A schematic would really be helpful here.

I really like this unit (for the gracious sacrifice it made), but I have no cash flow to buy a new unit or trade it in.

Any help would be greatly appreciated.

Thank you.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • dead
  • hardware
  • no_display
  • no_power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

I believe this one will start with no battery... It did in the past. Can't hurt to jump one in to see.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

We unfortunately can't give out schematics but if anyone else can help, please reply.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

I'm not sure about the BackUPS but some of APC's UPSes require a working battery to start up. See here.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:42 AM . Last Modified: ‎2024-03-21 04:04 AM

I believe this one will start with no battery... It did in the past. Can't hurt to jump one in to see.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore