Hello Guys,
I have a BX1400UI, which I use for my PC’s. I have connected the UPS to an external deep-cycle 80 AH battery, but the UPS shuts down after around 20 minutes, though it should stay on for a couple of hours.
I wonder if there is a way to make the UPS learn the higher capacity battery, or if there is a way to override the shut down.
Your help will be greatly appreciated.
Thanks,
Khaldoon
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:06 AM . Last Modified: 2024-03-26 03:40 AM
Hi Khaldoon,
The battery in the BX1400UI is not user replaceable so there is no way to amend the battery details on the UPS.
Regards,
Tom
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:06 AM . Last Modified: 2024-03-26 03:40 AM
Hi Khaldoon,
The battery in the BX1400UI is not user replaceable so there is no way to amend the battery details on the UPS.
Regards,
Tom
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.