BR650MI Counts down to hibernate or shut down, but does not shut down

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR650MI Counts down to hibernate or shut down, but does not shut down
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:20 AM

0 Likes
4
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:20 AM

BR650MI Counts down to hibernate or shut down, but does not shut down

While logged off, the Back-UPS can shut down the computer (this is good). While logged on in the case of AC power supply loss, it counts down to hibernate or shut down, and then nothing happens.

 

My question is:

How can the UPS be forced to shut down a computer that loses power while the user is logged in?

Additional notes:

Hibernate was disabled to allow shut down (after computer didn't hibernate after the  "the computer will hibernate in x seconds" message following removal of AC input to Back-UPS)

The shutdown /s  command works in the cmd window when run as an administrator by the logged in user.

 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

0 Likes
0
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

Hi Bill. 

Thanks for the response. The shutdown command was working from cmd (run as administrator). The Event viewer/windows logs/application was not showing any events with APC as the source after the countdown to shutdown popup showed (noted during commissioning a few days back).

The device was commissioned on a server that is rarely logged into. The UPS was found to function correctly only when one was not logged on to the server. The suggested fix has been applied over remote desktop but as I'm no longer on site,  there is no way to test that the fix works. The 2-off APC services restarted with local administrator login (in the Services window) after the fix was applied and the server was restarted.

What might be the likelihood, considering the suggested log in tab fix has now been applied to both APC services,  that the UPS shutdown command issued, while a user is logged in, will be able to shut down the PC?

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

0 Likes
0
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

Hi,

Are you running PowerChute Personal Edition 3.1? If not uninstall the current version and install version 3.1 There was an issue with version 3.0.1 that would prevent the system from shutting down when a user was logged in remotely. That issue was corrected with the release of version 3.1

When PowerChute is install hibernate is enable. To disable hibernate open a command prompt as an admin and enter powercfg.exe /hibernate off When hibernation is disable the system will power off. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

0 Likes
0
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

Thanks for the information Bill.

The BR650MI is running PowerChute Personal Edition 3.1.0 (installed with PCPE_3.1.0.exe).

When a user is logged in (not remotely), when AC power input is removed from the UPS:

1. It counts down the final 10 seconds advising of a pending hibernate if hibernate is enabled, before not hibernating.

2. It counts down the final 10 seconds advising of a shut down if hibernate is disabled, before not shutting down.

The computer is a HP EliteDesk 800 G3 SFF, running Windows 10.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

0 Likes
0
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

Hi,

Open the Control panel and go to Administrative tools, Event viewer, Windows logs, Application. PowerChute should record entries when the UPS switches to battery, when PowerChute causes hibernation, and when the event was handled successfully. The sources to look for are APC UPS Service and APC Data Service. If those items are logged the issue is being caused by something else running on the PC. 

You can test the shutdown command by opening a command prompt as an administrator and entering the command shutdown /h The system should hibernate. If the PC hibernates you should open the PowerChute services and changed them for system account to a local account that has administrative privileges. Go to Control panel, Administrative tools, services. You will see the 2 APC services. Right click on each and go to Log on. There you can change the type of account the service is using. Once the change has been made you will need to restart the server for the change to take affect.

In the example below I created a PowerChute user with admin privileges that the server is using. 

S5n5FxXve%2Bo58IkSdvS5xw%3D%3D.pngS5n5FxXve%2Bo58IkSdvS5xw%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:39 AM . Last Modified: ‎2024-03-26 03:19 AM

Hi Bill. 

Thanks for the response. The shutdown command was working from cmd (run as administrator). The Event viewer/windows logs/application was not showing any events with APC as the source after the countdown to shutdown popup showed (noted during commissioning a few days back).

The device was commissioned on a server that is rarely logged into. The UPS was found to function correctly only when one was not logged on to the server. The suggested fix has been applied over remote desktop but as I'm no longer on site,  there is no way to test that the fix works. The 2-off APC services restarted with local administrator login (in the Services window) after the fix was applied and the server was restarted.

What might be the likelihood, considering the suggested log in tab fix has now been applied to both APC services,  that the UPS shutdown command issued, while a user is logged in, will be able to shut down the PC?

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of