BR1500LCD - Unit placement and use with power strip

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR1500LCD - Unit placement and use with power strip
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

0 Likes
8
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

BR1500LCD - Unit placement and use with power strip

Hello,

I Just bought this fine UPS unit. A few questions before I set it up:

1) I know it is advisable not to place the UPS next to any serious electrical devices such as PC Monitor, etc. My question is whether it is ok to place the UPS on top of my PC tower?

2) Is it possible to use a decent extension power strip (such as this one: [http://www.newegg.com/Product/Product.aspx?Item=N82E16812120239]) in either of the following two ways:

i. Plug in the extension power strip to the wall outlet ==>> Plug in the UPS to the extension power strip == >> Plug in all equipment to UPS

ii. Plug in the UPS to the wall outlet ==>> Plug in the extension power strip to UPS ==>> Plug in all equipment to extension power strip

If both of these scenarios is possible, which is more advisable? Note that the extension power strip also offers very strong surge protection that is even better than the one offered by the UPS (extension power strip rates at 3540 joules!!!).

Thank you in advance.

David

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

KVAr said:

"Using a SURGE PROTECTOR on the output side of the UPS is not a good idea as the surge protector will try to absorb some power when the UPS goes on battery due to UPSs modified square wave output. It will reduce the life of your surge protector every time UPS goes to battery."

That can't be true! If that were true, many power supplies would go bad quickly when powered by an UPS. All the components found in surge protectors like "X" capacitors, "Y" capacitors, inductors and MOVs are also found inside many power supplies! The transient filtering stage componentes of a good power supplies are often better than those components found inside surge protectors, except the MOVs that come in bigger number on surge protectors, but that doesn't mean they'll start conducting energy when powered by stepped sine wave, or will they?? Please explain me why would an MOV stat conducting in this situation. If that is true, this shape of wave is not good for your power supply either, and nobody should use this kind of UPS anymore. If an UPS damages a surge protector, it WILL damage the PSU as well!

Btw, surge protectos do not absorb anything, they shunt overvoltages to neutral (which is grounded) and also to the safe ground (green - yellow/green) wire. MOVs do not absorve anything and those used on 120V surge protectos will only start conducting energy well above 120V. If an UPS is allowing more than 120V RMS while on battery, something is not right.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

David,

I would not place the UPS on top of the tower. Chances are the UPS weighs more than the tower, mainly because of the battery. If you can place them next to each other, should be fine, as that's how mine is setup currently with no interference.

As for question #2. Any non-apc surge protector whether upstream or downstream of the UPS voids the warranty and EPP as it introduces a problem of which manufacturer is liable for the surge.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

Thanks for your response.

OK, suppose I were to purchase an APC extension power strip. How would you now answer my second question?

Thanks again.

David

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

For an APC surge on #2, you'd want to use it downstream, unless you're only using the surge strip upstream for the UPS and nothing else. Downstream, if it goes into the battery backup side, make sure you don't exceed the VA capacity for the UPS. If on the surge side, there's no concern there.

If it's upstream of the UPS with other devices attached, they will all fight for power, increasing the possibility that the UPS goes to battery suddenly for no reason.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:20 PM

Sorry, I must be daft or something, lol.

Could you please explain what upstream and downstream means exactly. And as per your earlier answer, which option did you suggest that I use? 2.i or 2.ii?

Thanks.

David

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

Upstream means between the wall and the UPS. Downstream means between the UPS and the load.

I didn't formally choose 2.i or 2.ii because I'm unsure of your setup. If you have other equipment that's going between the wall and UPS on that surge strip, I'd advise against it. If you're plugging that equipment into the UPS and want to use the surge strip, just don't exceed the VA capacity on the battery outlets.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

"I know it is advisable not to place the UPS next to any serious electrical devices such as PC Monitor, etc. My question is whether it is ok to place the UPS on top of my PC tower?"

UPS will annoy CRT monitors, because CRTs are incredibly sensitive to magnetic fields, more so than just about anything else. You can put it next to just about everything else.

On top... no. that's dangerous. It makes the computer top heavy that it might topple over.

Using a SURGE PROTECTOR on the output side of the UPS is not a good idea as the surge protector will try to absorb some power when the UPS goes on battery due to UPSs modified square wave output. It will reduce the life of your surge protector every time UPS goes to battery.

A powerstrip.. like this is fine to use:
http://www.tigerdirect.com/applications/SearchTools/item-details.asp?EdpNo=3444827&Sku=T105-1260. This is what you want to do if you have a lot of wall warts for devices you want to be protected.

On the input side of UPS, despite what Notorious said, it's fine to use a power strip OR a surge protector.

"fighting for all the available power" is not a concern at all if you're using a power strip to power those low power devices running on wallwarts that takes up a substantial amount of space. It's a concern if you're going to connect your fridge, toater, microwaver, laser printer etc into it.

I have a router,a cable modem, external hard drives, a USB hub... each taking no more than 20W, but each one of them uses a wallwart, so I use a power strip to put them all under battery protection. Use a large power strip with spacing intended with wallwarts in mind or a power squid to power wallwarts. Don't plug them directly into the back of UPS as the warts might not fully and fall out.

Message was edited by: KVAr

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

>

A powerstrip.. like this is fine to use:
http://www.tigerdirect.com/applications/SearchTools/item-details.asp?EdpNo=3444827&Sku=T105-1260. This is what you want to do if you have a lot of wall warts for devices you want to be protected.

On the input side of UPS, despite what Notorious said, it's fine to use a power strip OR a surge protector.>
The warranty on the UPS won't be upheld with that upstream of the UPS. It would have to be an APC surge protector.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

0 Likes
0
1453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:19 PM

KVAr said:

"Using a SURGE PROTECTOR on the output side of the UPS is not a good idea as the surge protector will try to absorb some power when the UPS goes on battery due to UPSs modified square wave output. It will reduce the life of your surge protector every time UPS goes to battery."

That can't be true! If that were true, many power supplies would go bad quickly when powered by an UPS. All the components found in surge protectors like "X" capacitors, "Y" capacitors, inductors and MOVs are also found inside many power supplies! The transient filtering stage componentes of a good power supplies are often better than those components found inside surge protectors, except the MOVs that come in bigger number on surge protectors, but that doesn't mean they'll start conducting energy when powered by stepped sine wave, or will they?? Please explain me why would an MOV stat conducting in this situation. If that is true, this shape of wave is not good for your power supply either, and nobody should use this kind of UPS anymore. If an UPS damages a surge protector, it WILL damage the PSU as well!

Btw, surge protectos do not absorb anything, they shunt overvoltages to neutral (which is grounded) and also to the safe ground (green - yellow/green) wire. MOVs do not absorve anything and those used on 120V surge protectos will only start conducting energy well above 120V. If an UPS is allowing more than 120V RMS while on battery, something is not right.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore