Posted: 2025-12-09 12:24 PM
I have a BN1500M2 that started failing self tests and it was due to the battery. So I bought a new battery and just replaced it and ran a self test and the same thing happened. When it switches to the battery the run time will drop and then start alarming. Its a brand new battery. Does anyone know how to fix this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-09 11:16 PM . Last Modified: 2025-12-09 11:19 PM
The new RBC must be allowed to recharge for a minimum of 24-72 hours. Afterwards complete the following action items in sequence:
Brain Dead: https://www.se.com/be/fr/faqs/FA158947/
Connect the unit to a computer running APC Power Chute Software which you can download a copy using this resource link:
Date: Update the battery installation date as this will reset internal counters and adjust charging tables if applicable.
Self Test: Manually initiate a self test through power chute software and let pass and wait for the RBC (Replacement Battery Cartridge) to recover to 100% SOC (State of Charge).
Calibration: Manually initiate a battery calibration if available in Power Chute software (PCPE / PCSS) with a minimum of 30% or greater load.
Allow this procedure to complete and wait for the RBC to return to 100% SOC. This step will help the system better reflect the operational runtime and health of the RBC.
Report the results once all of the action items have been completed.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-09 11:16 PM . Last Modified: 2025-12-09 11:19 PM
The new RBC must be allowed to recharge for a minimum of 24-72 hours. Afterwards complete the following action items in sequence:
Brain Dead: https://www.se.com/be/fr/faqs/FA158947/
Connect the unit to a computer running APC Power Chute Software which you can download a copy using this resource link:
Date: Update the battery installation date as this will reset internal counters and adjust charging tables if applicable.
Self Test: Manually initiate a self test through power chute software and let pass and wait for the RBC (Replacement Battery Cartridge) to recover to 100% SOC (State of Charge).
Calibration: Manually initiate a battery calibration if available in Power Chute software (PCPE / PCSS) with a minimum of 30% or greater load.
Allow this procedure to complete and wait for the RBC to return to 100% SOC. This step will help the system better reflect the operational runtime and health of the RBC.
Report the results once all of the action items have been completed.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-10 08:24 PM
Everything is working as it should now! Thanks for the help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-11 04:23 AM
That’s great to here.
Rock On . . . 🤟