BE350G no power on battery side, no LEDs

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE350G no power on battery side, no LEDs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
117
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

0 Likes
7
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

BE350G no power on battery side, no LEDs

I have a BE350G that has worked great for the last year. This morning the LEDs are off, it is beeping once every ~4 seconds, the breaker was tripped. Only the surge protection side has power, there is no power on the battery side, LEDs are still off. The troubleshooting guide doesn't have anything that matches these conditions.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:31 AM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:31 AM

Hi,

Sorry for your inconvenience. Your unit is still under warranty so you should call technical support at 1-800-890-4272. They are available Monday - Friday 8 AM - 8 PM Eastern time. They will walk you through some troubleshooting steps and if the system does not come back on properly the unit will be replaced.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

Hello John,

Have you experienced any storms or power fluctuations recently? Also, what is the serial number of this unit?

Thanks, 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

Not that I am aware of. Serial # attached.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

0 Likes
0
1649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

Thanks for the info. 

There is two things that are going on here, first is the circuit breaker being tripped. This may be from too many things being plugged into the UPS. What all do you have plugged in?

The second is no power on the battery/surge side. To check this we can do what is called a cold start. To cold start we unplug the UPS from the wall and then attempt to power on a device from battery power alone. If the plugged in device does not turn on then we know the battery is going bad.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

There definitely weren't too many things plugged in. I haven't changed what is plugged in since I purchased the APC a year ago: 1 iMac and 1 CenturyLink wireless router on the battery side and 1 Asus monitor on the surge protection side.

I just attempted the cold start, with only the Asus monitor and an iPhone plugged into the battery side. No LEDs come on at any time (plugged in or not). If I press the power button, I get a beep, followed by a very quiet chirp a few seconds later. If I hold down the power button, I get a long beep or multiple beeps, and sometimes the iphone will give the "I'm charging" sounds very briefly, but then does not charge.

Afterwards, I plugged the APC back in. Again, there are no LEDs (regardless of whether I press the power button) and the unit beeps every 4 seconds. If I press the power button the beeping stops, still no LEDs.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:35 AM

Hello John,

Based off of the clod start and your iphone not charging for more than a few seconds, it definitely sounds like you have a bad battery. I can see that you have already contacted technical support to receive a new one, hopefully it will resolve your issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:31 AM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:31 AM

Hi,

I received & installed the replacement battery; however, the  unit is behaving exactly as it did with the old battery. Regards, John

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:31 AM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-27 12:31 AM

Hi,

Sorry for your inconvenience. Your unit is still under warranty so you should call technical support at 1-800-890-4272. They are available Monday - Friday 8 AM - 8 PM Eastern time. They will walk you through some troubleshooting steps and if the system does not come back on properly the unit will be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore