BACK UPS XS1000 has relay clicking sound

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BACK UPS XS1000 has relay clicking sound
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:07 PM . Last Modified: ‎2024-03-25 11:40 PM

0 Likes
2
960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:07 PM . Last Modified: ‎2024-03-25 11:40 PM

BACK UPS XS1000 has relay clicking sound

Unit is about 1 year old. "on Line " light on and operating. Every few seconds or minutes I hear a click from inside the unit, a relay opening or closing. It is a fairly loud click, but no lights change and nothing goes off. What is causing this click, and does it indicate a problem? I did some general searching for the problem, but have not found this problem yet.

Message was edited by: STEVE KEOWN

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:07 PM . Last Modified: ‎2024-03-25 11:40 PM

0 Likes
0
960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:07 PM . Last Modified: ‎2024-03-25 11:40 PM

well to start, do you have the powerchute software installed on a computer attached to the UPS?

I guess you can start by lowering the sensitivity on the UPS either via that software or the front panel of the UPS.

to do it via the front panel on the UPS, turn off your equipment attached then turn the UPS off. leave the UPS plugged into the wall. hold down the on/off button for ~10 seconds until all of the lights begin flashing on the front panel (to indicate programming mode) then quickly push the button until only one LED is flashing indicating it is on "low" sensitivity. alternatively, you can try "medium" by not pushing the buttons when two LEDs are flashing. three flashing indicates "high" sensitivity which is default.

sensitivity settings adjust the UPSs sensitivity to any type of voltage disturbance including High/Low/No RMS Voltage, Total Harmonic Distortion(THD), Change in voltage over Time(dv/dt), Frequency (Hz) out of tolerance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:07 PM . Last Modified: ‎2024-03-25 11:40 PM

0 Likes
0
961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:07 PM . Last Modified: ‎2024-03-25 11:40 PM

well to start, do you have the powerchute software installed on a computer attached to the UPS?

I guess you can start by lowering the sensitivity on the UPS either via that software or the front panel of the UPS.

to do it via the front panel on the UPS, turn off your equipment attached then turn the UPS off. leave the UPS plugged into the wall. hold down the on/off button for ~10 seconds until all of the lights begin flashing on the front panel (to indicate programming mode) then quickly push the button until only one LED is flashing indicating it is on "low" sensitivity. alternatively, you can try "medium" by not pushing the buttons when two LEDs are flashing. three flashing indicates "high" sensitivity which is default.

sensitivity settings adjust the UPSs sensitivity to any type of voltage disturbance including High/Low/No RMS Voltage, Total Harmonic Distortion(THD), Change in voltage over Time(dv/dt), Frequency (Hz) out of tolerance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:40 PM

0 Likes
0
960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-25 11:40 PM

If changing the sensitivity doesn't work, replace capacitor C41 with another 22uf capacitor.  That resolved the problem for me.  It is the equivalent to capacitor C60 on the UPS 800.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore