Avoiding blind faith with Powerchute Network Shutdown

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Avoiding blind faith with Powerchute Network Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:39 PM . Last Modified: ‎2024-03-21 02:38 AM

0 Likes
1
976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:39 PM . Last Modified: ‎2024-03-21 02:38 AM

Avoiding blind faith with Powerchute Network Shutdown

HI. I want to prove that I will get a clean shutdown with the settings I have configured. Can someone confirm if telling the Symettra UPS to switch to bypass with the "Signal PowerChute® Server Shutdown" box ticked should initiate a shutdown of the servers. My servers are set to shutdown on Battery Discharged and Bypass for maintenance (for purposes of this experiement.

I've tried it without success initiating the bypass from software. Should I do it from the UPS front panel and throw the bypass switches ?
Thanks
Martin

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 07:39 PM . Last Modified: ‎2024-03-21 02:38 AM

0 Likes
0
976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:39 PM . Last Modified: ‎2024-03-21 02:38 AM

It will not signal a shutdown when used with a Bypass command, per the following documentation under the Network Card help:

Signal PowerChute® Server Shutdown.

Select this option to notify all servers configured as "PowerChute® Network Shutdown clients" that are in communication with this UPS to shut down according to the values configured for "PowerChute® Network Shutdown Parameters". This option will not notify servers when performing any Bypass control actions.

You may want to use one of the other options such as UPS turn off, or UPS Reboot. Additionally, if you wanted a more "realistic" test, you could flip the input circuit breaker on the symmetra unit, which would force the UPS to battery, therefore starting an "on battery" notification on the NMC and and the on batt "countdown" on your PCNS clients. Once the computers have shut down based on your parameters, you can then flip the input circuit breaker on the UPS back on, and the UPS will go back to being online again. This test is nice because it not only tests your PCNS client settings, but the entire process from going to on battery, to NMC notification, to PCNS shutdown as if you actually had a power loss.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 07:39 PM . Last Modified: ‎2024-03-21 02:38 AM

0 Likes
0
977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:39 PM . Last Modified: ‎2024-03-21 02:38 AM

It will not signal a shutdown when used with a Bypass command, per the following documentation under the Network Card help:

Signal PowerChute® Server Shutdown.

Select this option to notify all servers configured as "PowerChute® Network Shutdown clients" that are in communication with this UPS to shut down according to the values configured for "PowerChute® Network Shutdown Parameters". This option will not notify servers when performing any Bypass control actions.

You may want to use one of the other options such as UPS turn off, or UPS Reboot. Additionally, if you wanted a more "realistic" test, you could flip the input circuit breaker on the symmetra unit, which would force the UPS to battery, therefore starting an "on battery" notification on the NMC and and the on batt "countdown" on your PCNS clients. Once the computers have shut down based on your parameters, you can then flip the input circuit breaker on the UPS back on, and the UPS will go back to being online again. This test is nice because it not only tests your PCNS client settings, but the entire process from going to on battery, to NMC notification, to PCNS shutdown as if you actually had a power loss.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now