Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Posted: 2021-06-29 06:59 PM . Last Modified: 2024-03-21 03:16 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:59 PM . Last Modified: 2024-03-21 03:16 AM
My search pulled up nothing, so:
Our local fire department says our new school building cannot receive an occupancy certificate until we replace the electrical connection for the computer carts.
Currently the carts use a 14/3 25' extension cord from the wall outlet to a cart-mounted APC Surge Protector. Hardware is plugged into the APC Surge Protector.
The Fire Dept Inspector says a Surge Protector with an integral 25' extension cord would be acceptable. APC does not provide such a product.
What to do?
Thank you,
Harry Jacobson
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:59 PM . Last Modified: 2024-03-21 03:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:59 PM . Last Modified: 2024-03-21 03:15 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:59 PM . Last Modified: 2024-03-21 03:15 AM
Harry,
The simplest setup here would be to nix the Surge Protectors on the cart and install a PanelMount Surge at the main service entry for the building. That'll be your 1 point of surge protection for the entire facility, eliminating the need for a seperate strip downstream.
After that, the 25' cord has nothing to do with the functionality of any APC equipment since the PMP is installed, therefore, it would be a discussion between the facility and the fire dept.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:59 PM . Last Modified: 2024-03-21 03:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:59 PM . Last Modified: 2024-03-21 03:15 AM
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.