Appropriate surge protection for classroom computer cart

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Appropriate surge protection for classroom computer cart
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:16 AM

0 Likes
2
1214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:16 AM

Appropriate surge protection for classroom computer cart

My search pulled up nothing, so:

Our local fire department says our new school building cannot receive an occupancy certificate until we replace the electrical connection for the computer carts.

Currently the carts use a 14/3 25' extension cord from the wall outlet to a cart-mounted APC Surge Protector. Hardware is plugged into the APC Surge Protector.

The Fire Dept Inspector says a Surge Protector with an integral 25' extension cord would be acceptable. APC does not provide such a product.

What to do?

Thank you,
Harry Jacobson

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:15 AM

0 Likes
0
1214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:15 AM

hjacobson wrote:
My search pulled up nothing, so:

Our local fire department says our new school building cannot receive an occupancy certificate until we replace the electrical connection for the computer carts.

Currently the carts use a 14/3 25' extension cord from the wall outlet to a cart-mounted APC Surge Protector. Hardware is plugged into the APC Surge Protector.

The Fire Dept Inspector says a Surge Protector with an integral 25' extension cord would be acceptable. APC does not provide such a product.

What to do?

Thank you,
Harry Jacobson
What exact did the fire inspector say was in a violation? I think the thing you're talking about is a power strip that is fairly common in schools for the carts they use with overhead projectors. which is a power strip with two or three outlets with a cord coming out that is 25' in length... instead of using a strip with a short cord + an extension cord.

That said, something like this might suite your need? and if you're concerned, you can use a surge protector on the cart downstream.
http://www.amazon.com/Tripp-Lite-TLM825GF-Safety-Yellow/dp/B000WJEUX2

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:15 AM

0 Likes
0
1214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:15 AM

Harry,

The simplest setup here would be to nix the Surge Protectors on the cart and install a PanelMount Surge at the main service entry for the building. That'll be your 1 point of surge protection for the entire facility, eliminating the need for a seperate strip downstream.

After that, the 25' cord has nothing to do with the functionality of any APC equipment since the PMP is installed, therefore, it would be a discussion between the facility and the fire dept.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:15 AM

0 Likes
0
1215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:15 AM

hjacobson wrote:
My search pulled up nothing, so:

Our local fire department says our new school building cannot receive an occupancy certificate until we replace the electrical connection for the computer carts.

Currently the carts use a 14/3 25' extension cord from the wall outlet to a cart-mounted APC Surge Protector. Hardware is plugged into the APC Surge Protector.

The Fire Dept Inspector says a Surge Protector with an integral 25' extension cord would be acceptable. APC does not provide such a product.

What to do?

Thank you,
Harry Jacobson
What exact did the fire inspector say was in a violation? I think the thing you're talking about is a power strip that is fairly common in schools for the carts they use with overhead projectors. which is a power strip with two or three outlets with a cord coming out that is 25' in length... instead of using a strip with a short cord + an extension cord.

That said, something like this might suite your need? and if you're concerned, you can use a surge protector on the cart downstream.
http://www.amazon.com/Tripp-Lite-TLM825GF-Safety-Yellow/dp/B000WJEUX2

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore