Another case of won't work with new batteries--Back-UPS NS 1250 LCD

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Another case of won't work with new batteries--Back-UPS NS 1250 LCD
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

0 Likes
3
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

Another case of won't work with new batteries--Back-UPS NS 1250 LCD

I have a Back-UPS NS 1250 LCD that is several years old. The batteries were shot so I replaced them with new Werker batteries, but it will not run on batteries for more than 2 minutes. The UPS passes all self tests and shows the batteries fully charged (on both the LCD and via PowerChute) after several hours. I did select "Replace Battery Date" in PowerChute. With a 30% load, it goes from full charge to no charge in only 2 minutes and shuts down. When connected back to power, it takes several hours to recharge again.

I have tried the manual recalibration technique several times--no change. Because it has no serial port (USB only), I cannot try the serial-based recalibration techniques.

Am I missing something? Is there some kinds of tests I can run to see what it might be doing or not doing (I do have voltmeters/scopes)? It there another way to accomplish the recalibration via a USB port?

Edit: voltage measured at the battery leads with the batteries disconnected is 27v.

Thanks in advance.

Message was edited by: JeffinMD

Message was edited by: JeffinMD

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

SOLVED--one of the new batteries was defective

I checked the voltage of each battery--more than 1 volt difference--not expected. I took the batteries back to BatteriesPlus, and they did a load test on each. The one battery with lower voltage did not pass the test. They handed me two new batteries and the UPS is now functioning correctly.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

As I'm sure you know, we don't recommend using 3rd party batteries although many customers have and they usually work. Besides voltage, what other specs do these batteries have? What about AMP hours

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

The replacement batteries are WKA12-8F2 12V 8Ah, slightly smaller amperage than the originals which were 9 Ah. I also replaced the batteries in Back-UPS XS 1300LCD at the same time with the same batteries and they work fine.

The OEM batteries in the 1250 were Center Power Tech 1290
The OEM batteries in the 1300 were B.B Battery HR1234W

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 PM . Last Modified: ‎2024-03-21 03:09 AM

SOLVED--one of the new batteries was defective

I checked the voltage of each battery--more than 1 volt difference--not expected. I took the batteries back to BatteriesPlus, and they did a load test on each. The one battery with lower voltage did not pass the test. They handed me two new batteries and the UPS is now functioning correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore