APC Backup UPS BX650CI-GR and HP ML350e gen8 with fixed power supply do not work together?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC Backup UPS BX650CI-GR and HP ML350e gen8 with fixed power supply do not work together?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

0 Likes
3
659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

APC Backup UPS BX650CI-GR and HP ML350e gen8 with fixed power supply do not work together?

Hi,

When the power fails in my house my server is backed with an APC BX650CI-GR. An all schuko socked model. As soon as the power fails the server shuts down, not gracefull but 2 seconds later totally down. I tried to find confirmation that i have a possible mismatch with the "new" power supply technology active PFC. On an other site there was an opinion that the server uses "active PFC" and while switching to "battery state" the server sees  "no current" because of an other output voltage wave. The OS I use is Windows 2012 server essentials R2 that sees the UPC as an (like a laptop) battery. I cannot use powershute in this OS in combination with USB to the UPC. The server has 96 gig of memory, two six core xeon's and uses a virtual harddisk (storage spaces mirror) of 40TB. I hope someone can help me out on fixing this issue or give me advice what APC model to use instread.

Cheers,

DutchAPCuser 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • gracefull
  • hp
  • mismatch
  • no
  • power
  • server
  • shutdown
  • supply
  • ups
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

Hi Gert,

It sounds as if the Power Supply is close to the UPSs maximum capability for supporting the attached load. Although the unit has been able to support the load adequately since March of 2015 as you've indicated, the battery has likely weakened as a result of supporting the heavy load for a long period of time.  As a result, it would appear the battery is now no longer capable of holding the server up long enough for the Graceful Shutdown to complete. I would recommend contacting your local support for help in determining whether or not the unit is under warranty and for assistance in procuring a replacement.

Secret Squirrel

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

Hi Gert,

It is possible the APFC is not happy with the Step Approximated Sinewave. Can you provide the model power supply you are using.

Additionally, when the server turned off did you see any visible indicators on the UPS or hear any audible tones? Did the UPS also turn off along with the server?

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

Hi Secret Squirrel,

The power Supply part number is:

685041-001 460 W power supply unit with ATX cable
assembly (68% efficiency)

At the first power (real) failure i was not present, but when i came in the green on off button was lid and a high pitch constant tone. 

HP power advisor shows that my server has an Utilization power of 439,62W (Max), idle power load is 128,3W. The output capacity is 390W (Source pdf APC) so i may be 49,62 short? In the same pdf APC states that it is a bad battery warning, the unit is sold to me at March 28, 2015.

Cheers, and many Thanks,

Gert

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

0 Likes
0
657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:00 AM . Last Modified: ‎2024-03-27 12:31 AM

Hi Gert,

It sounds as if the Power Supply is close to the UPSs maximum capability for supporting the attached load. Although the unit has been able to support the load adequately since March of 2015 as you've indicated, the battery has likely weakened as a result of supporting the heavy load for a long period of time.  As a result, it would appear the battery is now no longer capable of holding the server up long enough for the Graceful Shutdown to complete. I would recommend contacting your local support for help in determining whether or not the unit is under warranty and for assistance in procuring a replacement.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of