APC BackUPS Pro BR1500GI Squealing Noise with Water Heater

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC BackUPS Pro BR1500GI Squealing Noise with Water Heater
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
121
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
18
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

APC BackUPS Pro BR1500GI Squealing Noise with Water Heater

I just noticed that everytime I turn on our water heater, my BR1500GI UPS squeals continuously. Why is this happening?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

Ok so that tells us the issue is either with the water heater, the circuit in your house OR our units just don't work well with your situation. I've never heard of this issue and I'm not an electrician so I'm in no way blaming it on your water heater or house wiring but since we have ruled out our UPS being at fault(based on failure anyway), it may be worth having an electrician or someone qualified in that area to look at your circuit and/or water heater. I can only speak for the UPS and if it's been replaced, It's probably not the UPS

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 18
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

Ok but how about the buzzing noise that most members in this forum experience as long as the UPS is plugged in the outlet (whether it is on or off)?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

Sounds like an inrush issue to me. I would think a water heater would have a dedicated circuit, though apparently that is not always the case.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

Alright well i don't much about water heaters so I wasn't sure. Perhaps it causes an inrush and it overloads? Does this noise stay on the whole time? or Does it go away after a certain amount of time?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

I think the "squeal" the OP is reporting is the horn in the ups.

Not enough detail in the initial post but I would guess that turning on the water heater (electric?), is causing a voltage drop.

Just like a laser printer on the same line circuit as the ups. When the laser printer needs to heat up, it may cause the ups to complain about low voltage, maybe even switch to battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

It goes away when the person in our restroom finishes his/her shower, lol.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

There is no connection whatsoever between the two. You may want to contact tech support for your area although I honestly don't know how it's possible for this to happen.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

No, when I say squeal I do not mean the horn of the UPS. Yes, the Water Heater is electric and is connected on the same breaker as all other outlets (where the UPS is connected) in my home.

The voltage is never going LOW when I turn on the heater. It just affects the UPS and produces a whinning sound. Hmmm, I thought this whinning noise is very famous around this forum especially for this model? Other term for this sound is "buzzing". Here's a reference thread for you guys: http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/7937/instal... . There are many threads regarding that buzzing noise.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

What do you mean dedicated circuit? All electronics of one house connects to the main breaker, right?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

Well i mean that the water heater would have it's own dedicated breaker so that running it wouldn't directly affect other circuits in the house/building.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

The heater has its own breaker and the outlets (shorted to each other) have their own 20A breaker also. The brekaers all connect to the same metal rod in the distribution box though. Does that info present any new ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:25 AM

My thoughts: since the UPS is not connected to the water heater except by virtue of sharing the same electrical source, the cause is probably the water heater creating distortions on the AC line.

[This thread|http://forums.apc.com/spaces/4/back-ups-surge-protectors/forums/general/2655/smart-ups-1500-shown-as...] has a good discussion of the topic.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:24 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:24 AM

Makes sense to me. Unfortunately, it's hard to confirm that unless you have an electrician that can test for distortion etc. With a solution this small, it may or may not be worth doing that though.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:24 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:03 AM . Last Modified: ‎2024-03-21 04:24 AM

So this means I have no choice but to bear with the sound?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

Well we have a few questions we(APC) can't answer.

Is the water heater causing distortion on the line?
Is this distortion normal? and if not, can it fixed?

I am curious what would happen if you installed our software on your computer, and saw what the software said when this was happening. Is That something you'd be willing to test?

Link to PowerChute Personal Edition

http://www.apc.com/tools/download/software_comp.cfm?sw_sku=SFPCPE302&id=129&family=&part_num=&swfam=...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

How do I know if my water heater is causing distortion on my line? What do I need to measure as basis?

The software is already installed in my PC even before asking this issue in this forum. It doesn't say anything when the buzzing sound happens. There is NOT even a significant voltage fluctuation caused by the water in order for the UPS' AVR to kick-in. The UPS is indicating normal operation and very good input and output voltages. When I turn on the water heater, there's only around 1 to 2 volts input voltage drop from the state when it is off.

I hope this is significant information from my side.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

I'm not an electrician so I'm not really sure how to test for it. Though you do have the biggest "back up" we make, it's still a very basic unit and doesn't have the reporting capability of our larger units. With our smart ups and smart ups online line, the software shows us more in depth information such as voltage every minute etc. That being said, there is no evidence that a better unit, such as a smart ups, would work better in this situation since we're not sure what is actually causing this issue. At this point, it's probably worth getting a replacement unit to see if the UPS is the problem though I suspect it's not the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

I already RMA'd this unit thrice and got a brand new unit thrice which have the same problems also.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

0 Likes
0
2080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 AM . Last Modified: ‎2024-03-21 04:24 AM

Ok so that tells us the issue is either with the water heater, the circuit in your house OR our units just don't work well with your situation. I've never heard of this issue and I'm not an electrician so I'm in no way blaming it on your water heater or house wiring but since we have ruled out our UPS being at fault(based on failure anyway), it may be worth having an electrician or someone qualified in that area to look at your circuit and/or water heater. I can only speak for the UPS and if it's been replaced, It's probably not the UPS

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore