2 Back UPS ES 500 with different issues

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • 2 Back UPS ES 500 with different issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:41 AM . Last Modified: ‎2024-03-22 03:10 AM

0 Likes
4
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:41 AM . Last Modified: ‎2024-03-22 03:10 AM

2 Back UPS ES 500 with different issues

First one: Turn on, get green on light then you hear random click like a circuit opening and closing

Second One: Turn on and the green light just blinks

Any thoughts please?

Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

0 Likes
0
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

i also have the problem of the constant beeping sound that i cant get to keep quiet. how do i make it silent and also stop the blinking green. the model is BE 500R-AS and the serial number is 5B0819T19262. please get back ASAP. thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

0 Likes
0
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

Ed,

Regarding the first unit issue, please make sure that the input power to the unit is normal. The relay inside the UPS may be audible in some environment when it transfers from on line to on battery or on battery to online. Is the UPS providing the power to the connected equipment when it is making clicking sound? If possible, could you please adjust the UPS sensitivity to Low and check if it helps?
How old Is this unit?

I would like to gather some more information regarding the second UPS issue. Could you please let me know the exact Model and Serial number of the UPS? you can find these details on a white bar code sticker at the bottom of the unit. The reason I am asking the exact model and serial number of UPS is to find the status of the unit. Is the UPS beeping constantly when the green light is blinking?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

0 Likes
0
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

sir i have a problem also about that clicking sound of my ups and i saw your post. You said that try to adjust the sensitivity and i dont know how to adjust it

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

0 Likes
0
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

Hi Jurome,

Can you tell us the exact model number of your UPS? Also, if you can install the APC PowerChute Software and the UPS can be connected to a PC via the USB cable the software can be used to adjust the sensitivity.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:42 AM . Last Modified: ‎2024-03-22 03:10 AM

i also have the problem of the constant beeping sound that i cant get to keep quiet. how do i make it silent and also stop the blinking green. the model is BE 500R-AS and the serial number is 5B0819T19262. please get back ASAP. thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore