symmetra px communication lost with metering board.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • symmetra px communication lost with metering board.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
6
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

symmetra px communication lost with metering board.

symmetra px communication lost with metering board.
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

Thanks Bill!

I get that the power modules are a half bridge rectifier inverter so it needs two 192v sources. By the way, I think you are right, I think its the right thing to buy a new rack of batteries. I will be in contact with you.

Thanks for your replies, I appreciate your help.

Sincerely Mh, Fazail Waasai DABS SCADA member.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

Hi,

I asked the 3 Phase support team in in North America and they recommend you contact 3 phase support in your region for assistance. 

Here is a link to the main contact page for Schneider Electric support http://www.apc.com/us/en/support/contact-us/index.jsp After opening the link change the country to your location and you will be provided call in information along with an e-mail option. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

Thanks Bill!

I did contact with APC authorities in here, they did come and checked the UPS, They said you need to change the batteries, the question is, Do power modules need batteries to start?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

Hi,

A PX actually wont boot up correctly without batteries installed.  It used the DC bus to properly turn on the power modules, and if not there, the screen will certainly light up, but the UPS will have a “Start-UP Configuration Fault” and never be able to run online.  Typically for long term running you would maintain at least a 1 power mod : 1 battery row ratio.  So in practice for  booting up as well.  If you do not have a 1 to 1 ratio just keep extra power modules turned off. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

Thanks Bill!

Our APC has 6 Rows of battery, In 1 Row of batteries, 4 Battery module each with 8 12v 9A Cells, each module 96v 9A (I bet you already know that). unfortunately all batteries are failed.

Can I Energize the DC Bus using a 192v external DC power bank to get sure the Power modules are fine and the main problem is the battery modules?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

Hi,

Our recommendation would be to purchase a single row of (4) SYBTU2-plp batteries and attempt to start the UPS with one power module,  and then boot up the rest of the power modules from there.  The UPS was designed and tested with VRLA batteries as the DC power source, so we cannot recommend the use of other DC power. 

That being said, do keep in mind that this is a midpoint battery system. At your DC terminals at the back of the UPS you have Positive(+), Center/Midpoint(C), Negative(-).  You would have 192V nominal DC from Pos to Center, and another 192VDC from Center to Negative.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:10 PM

Thanks Bill!

I get that the power modules are a half bridge rectifier inverter so it needs two 192v sources. By the way, I think you are right, I think its the right thing to buy a new rack of batteries. I will be in contact with you.

Thanks for your replies, I appreciate your help.

Sincerely Mh, Fazail Waasai DABS SCADA member.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore