snmp and self test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • snmp and self test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

0 Likes
6
2144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

snmp and self test

Hi folks,

Smart-UPS RT 2000 RM XL

I'm monitoring some ups from APC and while it works finely, the ups starts a self test every 15 days. Well, raising up an alert from Nagios.

So my question, is there a way to match the self test state via snmp ?

From powermib, upsBasicStateOutputState (1.3.6.1.4.1.318.1.1.1.11.1.1.0),

...

Flag 27: Self Test In Progress

...

But during the self test, I just get flag 29  (Graceful Shutdown Issued by Upstream Device) and
Flag 2 (On Battery) up.

Any idea ?

jeff

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

No problem laughing that MIB is 10 years old now though I saw.

You'll find our latest MIB @  http://www.apc.com/tools/download/index.cfm and select Firmware Upgrades - MIB to filter by software/firmware. I think the latest version is 4.0.9 or 4.1.0..?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

Can you clarify what UPS Network Management Card model is in your UPS? And what firmware is on that device?

Are you strictly limited to polling (response/request) or are you able to utilize SNMP traps (notifications) too?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

Hi Angela,

some data collected from my UPS :

Smart-UPS RT 2000 RM XL

SNMPv2-SMI::enterprises.318.1.1.1.1.2.1.0 = STRING: "418.8.I"
SNMPv2-SMI::enterprises.318.1.1.1.1.2.2.0 = STRING: "11/08/11"
SNMPv2-SMI::enterprises.318.1.1.1.1.2.3.0 = STRING: "QS1146330043"

SNMPv2-SMI::enterprises.318.1.4.2.4.1.2.2 = STRING: "ZA1151002558"
SNMPv2-SMI::enterprises.318.1.4.2.4.1.3.1 = STRING: "apc_hw05_aos_517.bin"
SNMPv2-SMI::enterprises.318.1.4.2.4.1.3.2 = STRING: "apc_hw05_sumx_517.bin"
SNMPv2-SMI::enterprises.318.1.4.2.4.1.4.1 = STRING: "v5.1.7"

Hope it is enough.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

And yes, i'm strictly limited to polling.

Any news btw ?

jframeau

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

Sorry for the delay.

What I have access to is a v5.1.7 NMC in a Smart UPS 3000. So it is a slightly different UPS.

I queried my UPS for this OID before I did anything and got:

0001010000000000001000000000000000000000000000000000000000000000


And if I counted correctly, that means:

  • Flag  4: On Line  
  • Flag  6: Serial Communication Established
  • Flag 19: On


Then, I did a self test on the UPS and got:


0100010000000000001000000000100000000000000000000000000000000000

  • Flag  2: On Battery
  • Flag  6: Serial Communication Established
  • Flag 19: On
  • Flag 29: Self Test In Progress  


Now, my first thought here having the experience that I have is that each UPS and UPS type is implemented differently sometimes. So I decided to track down an RT to try.


The closest thing I have to that is a Smart UPS RT 1500 which is the NAM version of what you have I think but it had an AP9619 in it at v3.7.2. I suspect it'd be the same as I type this.


I queried it and got this before I did anything:

0001010000000000001000000000000000000000000000000000000000000000


Seems to be flags 4, 6, and 19 again.


I did the self test on this unit and got:


0100010000000000001000000000100000000000000000000000000000000000


And I am seeing the same thing again with Flag 29 showing.


Then, I contacted our overseas support team to find an SURT1000XLI which should be closer. It has a Network Management Card 2 in it but it is at v6.1.1.


I got: 0001010000000000001000000000000000000000000000000000000000000000


4, 16, 19.


I did a self test and got:


0100010000000000001000000000100000000000000000000000000000000000


So 29 is there too!



Now by the time I got through all of this, I am realizing that you see flag 27 as Self Test in Progress but I see Flat 29 as this. What version of the MIB are you referencing? I was looking at 4.0.9:


  •        Flag 27: Warning Battery Temperature
  •        Flag 28: Critical Battery Temperature
  •        Flag 29: Self Test In Progress  
  •        Flag 30: Low Battery / On Battery
  •        Flag 31: Graceful Shutdown Issued by Upstream Device
  •        Flag 32: Graceful Shutdown Issued by Downstream Device


So, maybe this is really all fine and just there is confusion over what the flag numbers are??


Another option might be .1.3.6.1.4.1.318.1.1.1.4.1.1 or ups.upsOutput.upsBasicOutput.upsBasicOutputStatus but I tested it and it reported "on battery" versus battery test..There may be a few other options we can look at too if the issue here is just with the flag numbering.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

0 Likes
0
2145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

Thx very for the help !

The mib I was referencing is at http://support.ipmonitor.com/mibs/POWERNET-MIB/raw.aspx.

And flag 27 is given for "Flag 27: Self Test In Progress" . Bad ....

I apologize for the noise.

jeff




Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

0 Likes
0
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:36 AM . Last Modified: ‎2024-03-05 12:33 AM

No problem laughing that MIB is 10 years old now though I saw.

You'll find our latest MIB @  http://www.apc.com/tools/download/index.cfm and select Firmware Upgrades - MIB to filter by software/firmware. I think the latest version is 4.0.9 or 4.1.0..?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore