smart-ups 1500 product id and product key not available

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • smart-ups 1500 product id and product key not available
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
TomMetz
TomMetz
Cadet

Posted: β€Ž2025-01-16 10:44 AM

0 Likes
4
1103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-01-16 10:44 AM

smart-ups 1500 product id and product key not available

I can't register a smart-ups 1500 from 2017, QR code is not available and I don't know how the get the product id and key. Thanks a lot

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: β€Ž2025-01-17 07:23 AM

0 Likes
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-01-17 07:23 AM

Hi Tom,

 

Please review this APC Resource Link:

 

https://www.apc.com/ca/en/faqs/FA364281/

 

Questions Ask - If not, and this reply provided the answer kindly mark this as a solution so it may help the next person asking the same. πŸ‘

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2025-01-22 01:01 AM

In response to TomMetz
0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-01-22 01:01 AM

Hi Tom,

 

Just to be clear on your question about registering your UPS system. If this is for warranty purposes you can follow this APC Resource Link:

 

https://www.apc.com/ca/en/support/product-support/registration-warranty-services.jsp

 

If this is for the APC Smart Connect Portal (Cloud) Service. Only devices that have a letter (C) at the end of their serial number are Smart Connect enabled.

 

You can tell by the dedicated green coloured RJ45 Ethernet port on the back of the UPS system. If not present you can not use this cloud service.

There will also be a QR code that you can scan with your smart phone that is typically affixed to the top, side, front of the exterior of the frame.

 

 Questions Ask . . . πŸ‘

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
PowerChuteTester
Crewman PowerChuteTester
Crewman

Posted: β€Ž2025-01-17 06:18 AM

0 Likes
2
1060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-01-17 06:18 AM

@TomMetz 

 

The product ID and Key will be on a sticker attached to the UPS. If the UPS is a SMT or SMX model UPS you will also find the product ID and Key via the LCD panel. Go to About and scroll up or down until you see the info.

 

BTY: If the model of your UPS does not end with C the UPS is not a SmartConnect UPS. Examples: SMT1500C, SMC1500C, SMT1500RM2UC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2025-01-17 07:23 AM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-01-17 07:23 AM

Hi Tom,

 

Please review this APC Resource Link:

 

https://www.apc.com/ca/en/faqs/FA364281/

 

Questions Ask - If not, and this reply provided the answer kindly mark this as a solution so it may help the next person asking the same. πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

TomMetz
TomMetz
Cadet

Posted: β€Ž2025-01-21 11:59 PM

In response to PowerChuteTester
0 Likes
1
1006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-01-21 11:59 PM

Thanks a lot for your answer, Crewman, and sorry for my later answer - I was traveling.

I have a SMT1500I with an installed NMC from 2017.

On the back site is only a sticker with the UPS type and the serial number. Also in the menu under Info (I'm using the German language version) you can find only the TeileNr. (UPS type: SMT1500I), SerienNr.: 3S1716X05566 and the Firmware version 15.0 / ID18 - I upgraded the firmware from the former version 9.x when I changed the battery two weeks ago.

So the question is: can I register this a little bit older UPS, it is running fine, no reason to change it.

Of course the next question is, if I really need to register it.

Thanks again for your support.

Tomas

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2025-01-22 01:01 AM

In response to TomMetz
0 Likes
0
1004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-01-22 01:01 AM

Hi Tom,

 

Just to be clear on your question about registering your UPS system. If this is for warranty purposes you can follow this APC Resource Link:

 

https://www.apc.com/ca/en/support/product-support/registration-warranty-services.jsp

 

If this is for the APC Smart Connect Portal (Cloud) Service. Only devices that have a letter (C) at the end of their serial number are Smart Connect enabled.

 

You can tell by the dedicated green coloured RJ45 Ethernet port on the back of the UPS system. If not present you can not use this cloud service.

There will also be a QR code that you can scan with your smart phone that is typically affixed to the top, side, front of the exterior of the frame.

 

 Questions Ask . . . πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore