power consumption of UPS with respect to battery charging

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • power consumption of UPS with respect to battery charging
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
VIK
VIK
Cadet

Posted: β€Ž2024-04-17 06:09 PM

0 Likes
2
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-04-17 06:09 PM

power consumption of UPS with respect to battery charging

Hi..

Please help me understand below situation:-

For Industrial UPS, say Galaxy VS of 20KW, the data sheet says it has efficiency of ~96% at normal operation on 400V and the battery charging power is ~20%. Also, suppose my total connected load on output side is ~15KW.

Now does it mean:

a) maximum load that can be connected at output is 96% of 20KW i.e. 19.2KW ? Meaning we can still connect more load from 15KW to upto 19.2KW ?

b) battery charging power consumption is 20% of 19.2KW i.e. 3.84KW ?

c) input power to UPS is sum of its output to load and battery charging power ?

d) input power consumption of this 20KW UPS, to be given to feeder supplier of the Building Power System shall be 20KW ? or it shall be 23.04KW (19.2 KW as max load and 3.84KW as battery charging power) ?

 

Kindly reply item wise.

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
dpierce4776
Lieutenant dpierce4776
Lieutenant

Posted: β€Ž2024-04-19 05:20 AM

0 Likes
1
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-04-19 05:20 AM

Typically speaking no electric device can take more than 80% of its input breaker size. In your case APC calls for a 40 amp input breaker and a 32 amp bypass breaker. So you would take the lower of these for load as the extra 8 amps on the input is reserved for charging the batteries under normal operation.

 

On top of that you have to also consider that the UPS in question can only handle up to 20KVA. Which is not "sustained" meaning that while it can "handle 20KVA" it should not be the goal. With all electrical devices the 80% rule for steady load should be maintained. 

For a UPS 4 things must always be considered.

  1. The running load should not exceed 80% of the total UPS rating.
  2. All breakers (rule of thumb) will trip under sustained loads of 80% of there rating.
  3. If input and bypass breakers differ in size all calculations for sustained loads should be made using the lower of the two.
  4. Battery charging is on top of total load in amps. and is usually a percentage of the total, not the variable load.   

 

Also I am not seeing in the data sheet where it says "battery charging power is ~20%" But all things considered that would be 20% of the total load on the input breaker. Not 20% of whatever load you have. So for a 20KVA UPS you can for rule of thumb use 4amps (20% of 20KVA in a perfect world of a 1 to 1 power factor)

So your total load calculation should be roughly total load amps = load amps + 4 amps. Since the bypass breaker is 32 amps your total load should not exceed 80% of that or 25 amps for the breaker, as well as 80% of the UPS rating which is ~16KVA or 25 amps. KVA is not usually equal to KW unless in a 1 to 1 power factor ratio which almost never happens.

If you are running 15KW that with a 400 volt system that works out to be 21.7 amps. Add your 4 amps for charging and you have 25.7 amps. I would not add anymore to the UPS it is fine under normal operation as you input breaker of 40 amps can handle that. But if you go to bypass of any reason you will be playing with tripping the breaker and dropping the load.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
dpierce4776
Lieutenant dpierce4776
Lieutenant

Posted: β€Ž2024-04-19 05:20 AM

0 Likes
1
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-04-19 05:20 AM

Typically speaking no electric device can take more than 80% of its input breaker size. In your case APC calls for a 40 amp input breaker and a 32 amp bypass breaker. So you would take the lower of these for load as the extra 8 amps on the input is reserved for charging the batteries under normal operation.

 

On top of that you have to also consider that the UPS in question can only handle up to 20KVA. Which is not "sustained" meaning that while it can "handle 20KVA" it should not be the goal. With all electrical devices the 80% rule for steady load should be maintained. 

For a UPS 4 things must always be considered.

  1. The running load should not exceed 80% of the total UPS rating.
  2. All breakers (rule of thumb) will trip under sustained loads of 80% of there rating.
  3. If input and bypass breakers differ in size all calculations for sustained loads should be made using the lower of the two.
  4. Battery charging is on top of total load in amps. and is usually a percentage of the total, not the variable load.   

 

Also I am not seeing in the data sheet where it says "battery charging power is ~20%" But all things considered that would be 20% of the total load on the input breaker. Not 20% of whatever load you have. So for a 20KVA UPS you can for rule of thumb use 4amps (20% of 20KVA in a perfect world of a 1 to 1 power factor)

So your total load calculation should be roughly total load amps = load amps + 4 amps. Since the bypass breaker is 32 amps your total load should not exceed 80% of that or 25 amps for the breaker, as well as 80% of the UPS rating which is ~16KVA or 25 amps. KVA is not usually equal to KW unless in a 1 to 1 power factor ratio which almost never happens.

If you are running 15KW that with a 400 volt system that works out to be 21.7 amps. Add your 4 amps for charging and you have 25.7 amps. I would not add anymore to the UPS it is fine under normal operation as you input breaker of 40 amps can handle that. But if you go to bypass of any reason you will be playing with tripping the breaker and dropping the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

VIK
VIK
Cadet

Posted: β€Ž2024-04-24 04:36 PM

In response to dpierce4776
0 Likes
0
1356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-04-24 04:36 PM

Thanks a lot for such a detailed explanation πŸ™ πŸ™, much appreciated !!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of