pcns VM can not be deployed on a single VMware ESXi 6.7 / /.0 U3 Host "Could not connect to Host over the network."

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • pcns VM can not be deployed on a single VMware ESXi 6.7 / /.0 U3 Host "Could not connect to Host over the network."
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Naiden
Crewman Naiden
Crewman

Posted: ‎2023-05-15 04:06 AM . Last Modified: ‎2023-05-15 04:30 AM

0 Likes
11
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-15 04:06 AM . Last Modified: ‎2023-05-15 04:30 AM

pcns VM can not be deployed on a single VMware ESXi 6.7 / /.0 U3 Host "Could not connect to Host over the network."

I have a strange problem here and hope that I can get help.

We have several VMware ESXi 6.7 and 7. U3 hosts.

Three of the hosts are connected to a APC UPS in location A and the other three are connected to another APC UPS in location B.

The first 3 active hosts in location A are managed by a VCenter.

I imported a PowerChute Business Edition VM Version 5 on each of the hosts and want to configure the PowerChutses VMs on each host and UPS.

The problem: The three hosts that are managed by Vcenter are configured cleanly in the steps of the configuration wizard of the PowerChuite.

The three hosts that are standalone and not connected to the VCenter are not found in the configuration wizard of the PowerChute ‘Could not connect to Host over the network.’ Of course I enter in the individual steps as type standalone server.

It doesn’t matter if the PowerChute VMs are deployed via the VCenter or via the ESXi host and on with of the hosts.

 

What is the reason for this?

Thanks for your help

 
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
malinoskikev
malinoskikev
Cadet

Posted: ‎2023-05-15 07:14 AM

0 Likes
0
3607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-15 07:14 AM

I am running into the same issue. To add more to this, I am prompted to accept a certificate warning from the ESXi host I am trying to connect to. When I accept the SSL error I get "Could not connect to Host over network."

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-05-15 07:23 AM

0 Likes
0
3607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-15 07:23 AM

@Naiden 

 

Please send a screenshot of the error that is displayed. And note that when installing PCNS 5 on a standalone ESXi host, you must start the PowerChute service before the PNCS web interface becomes available. 

 

To start the PowerChute service, log into the PowerChute VM as root. Enter the commands systemctl enable PowerChute. Then enter systemctl start PowerChute.

 

As for the ESXi host not discovered with configuring with vCenter, only hosts managed by vCenter will be found when configuring PowerChute with vCenter Server. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Naiden
Crewman Naiden
Crewman

Posted: ‎2023-05-15 08:10 AM . Last Modified: ‎2023-05-15 08:29 AM

0 Likes
0
3604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-15 08:10 AM . Last Modified: ‎2023-05-15 08:29 AM

ESXi 7.0 U3 stand alone Server

Deployment PCNS_en_5.0.0.ova in the ESXi Web GUI

Go through the Configuration wizard in the console

After deployment login as root in the console

cd /opt/APC/PowerChute/group1

vi pcnsconfig.ini

username= new user name

password= new password

systemctl enable PowerChute

systemctl start PowerChute

systemctl status PowerChute

 

 configuration wizard  https://IP:6547

On Picture 3 I click for accept certifcate

In Step 4 no connection to host possible

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-05-16 10:33 AM

0 Likes
0
3557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-16 10:33 AM

@malinoskikev 

 

Do you have a domain name server and if so can you ping the ESXi using the domain name from the PCNS VM?

If you can ping the ESXi host using the domain name stop the PowerChute service (asystemctl stop PowerChute) edit /etc/hosts and add the ESXi host domain name and IP address.

 

Example of the hosts file:

127.0.0.1 localhost localhost.localdomain localhost4 localhost4.localdomain4
::1 localhost localhost.localdomain localhost6 localhost6.localdomain6
192.168.0.141 ESXiHost141.TestLab.local 

Reply

Link copied. Please paste this link to share this article on your social media post.

Naiden
Crewman Naiden
Crewman

Posted: ‎2023-05-16 03:42 PM

0 Likes
0
3550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-16 03:42 PM

Hello and thank you for your support.

We assumed that the problem would be properly investigated :-(.

This is not a DNS problem. As I already described in the initial post, we have three other ESXi hosts that are configured exactly the same way, but are managed by one VCenter and there the configuration of the PowerChute as a single host works without any problems!

 We still edited the host file on one of the PowerChute VMs according to your instructions (yes, we have our own DNS servers and they are also configured in the network settings of the PowerChute) and unfortunately the error did not change, no matter if we enter the IP address of the ESXi host or the DNS name in the setup in the web GUI.

Please investigate the problem. It must be a bug in the software.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-05-17 05:12 AM . Last Modified: ‎2023-05-17 07:37 AM

0 Likes
0
3519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-17 05:12 AM . Last Modified: ‎2023-05-17 07:37 AM

@Naiden 

 

Would you send a copy of the error log and debug log that will be found in /opt/APC/PowerChute/group1? And, where is the system located? Country is fine. We do not need the specific location. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Naiden
Crewman Naiden
Crewman

Posted: ‎2023-05-17 09:40 AM

0 Likes
0
3507
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-17 09:40 AM

we had to start the ssh deamon first

systemctl start sshd

Location is Germany

Attachments
error.log
debug.log
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-05-17 11:36 AM

0 Likes
3
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-17 11:36 AM

@Naiden 

 

The issue is due to CN value in the SSL cert the ESXi host is providing. The CN value is being set to localhost.localdomain. To avoid this we added the following entry to the /etc/hosts file;

 

< ESXi host IP >     localhost          localhost.localdomain

 

Example: 

192.168.0.141 localhost       localhost.localdomain

 

That will allow the connection to proceed.

 

A long-term solution would be to add the host to vCenter to generate a cert signed by vCenter CA or replace the default ESXi host cert with a signed cert and then add the signed cert to the PowerChute keystore.

Reply

Link copied. Please paste this link to share this article on your social media post.

dg25
dg25 Cadet
Cadet

Posted: ‎2023-05-19 04:31 AM . Last Modified: ‎2023-05-19 12:06 PM

In response to BillP
0 Likes
1
3457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-19 04:31 AM . Last Modified: ‎2023-05-19 12:06 PM

@Naiden @BillP 

 

During the installation of ESXi, the installer generates a self-signed certificate for each ESXi host, but the process is performed before the ESXi identity is configured. This means the ESXi host has a common name in the self-signed certificate of localhost.localdomain.

Instead of adding < ESXi host IP > localhost localhost.localdomain to the PowerChute VM's hosts file, after assigning a domain name to the ESXi host, regenerate the hosts' self-signed certificate.

To re-generate the self-signed certificate:

Login to the ESXi host over SSH (Requires ESXi shell and ssh access to be enabled on the host)

Back up the existing cert files:

        mv /etc/vmware/ssl/rui.crt /etc/vmware/ssl/rui.crt.old

        mv /etc/vmware/ssl/rui.key /etc/vmware/ssl/rui.key.old

Generate a new cert that contains the FQDN for the CN value. - /sbin/generate-certificates

Restart the hostd service on the host - /etc/init.d/hostd restart

Reply

Link copied. Please paste this link to share this article on your social media post.

dg25
dg25 Cadet
Cadet

Posted: ‎2023-05-19 04:33 AM

In response to dg25
0 Likes
0
3457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-19 04:33 AM

Adding the Hosts to vCenter would also generate a new cert signed by VMware Root CA with IP address or FQDN set as the CN value.

Reply

Link copied. Please paste this link to share this article on your social media post.

Naiden
Crewman Naiden
Crewman

Posted: ‎2023-05-20 07:49 PM

In response to BillP
0 Likes
0
3428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-20 07:49 PM

Thank you. Problem is solved 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore