help with configuring NMC3 and PCNS 5.1

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • help with configuring NMC3 and PCNS 5.1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
rpremuz
rpremuz
Cadet

Posted: ‎2025-02-17 01:09 AM

0 Likes
1
541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 01:09 AM

help with configuring NMC3 and PCNS 5.1

Hi!

 

We have a new APC SmartUPS X 3000 with 15.0 firmware and Network Management Card 3 (model AP9640 with su v2.5.0.6, aos v2.5.0.8, boot v1.5.1.1).

The UPS will be used to power:

  • on Outlet Group 1 - some network devices (Internet router etc.)
  • on Outlet Group 3 - a couple of Windows servers with APC PowerChute Network Shutdown 5.1 installed

I need help with configuring the NMC and PCNS (via web UI) for the following scenario:

  • When the UPS is on battery and the runtime of the UPS drops to 10 minutes:
    - PCNS on each server initiates shutdown of the server
    - after 5 minutes Outlet Group 3 turns off (the servers needs up to 5 minutes to shut down)
  • When the UPS is on battery and the runtime of the UPS drops to 2 minutes:
    - the Outlet Group 1 turns off
  • When input power returns:
    - the UPS turns on Outlet Group 1 after 1 minute (which turns on the network devices)
    - the UPS turns on Outlet Group 3 after 3 minutes (which starts the servers as they are configured to start automatically after power is connected to their PSUs)

Which parameters should be set in Outlet Groups Configuration and Shutdown Configuration on the NMC and how to configure PowerChute event actions on PCNS installed on the servers?

 

Also, if the input power returns after each PCNS initiates shutdown of a server but the Outlet Group 3 is still turned on, will NMC turn off the outlet group after set 5 minutes anyway, and then turn it on after 3 minutes?

 

In User Guide - PowerChute Network Shutdown v5.1 - Standard I have read the Event Configuration section but I find it vague. For example, it starts with "When UPS events occur, PowerChute can be configured to log the event, notify users, execute a command file or initiate a system shutdown through the Configure Events screen." So, on a server I configured only the shutdown action for Runtime exceeded event in PowerChute, but then I noticed that when NMC loses communication with PowerChute (for example because the server is restarted), NMC initiates shutdown of all outlet groups! This is very unexpected behavior and it is not mentioned anywhere in the User Guide.

 

-- rpr.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
rpremuz
rpremuz
Cadet

Posted: ‎2025-02-18 05:53 AM

0 Likes
0
489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-18 05:53 AM

I am trying to figure out the shutdown scenario given in User Guide - PowerChute Network Shutdown v5.1 - Standard, section "UPS with Outlet Groups", Example 1: Turn off Outlet Group enabled, no shutdown command file configured:

 

1. PowerChute reports that the UPS is on battery.

 

2. After the shutdown delay configured for the On Battery event has elapsed PowerChute sends a command to turn off the outlet group that PowerChute is registered with.

Where is the shutdown delay option configured? I can't find it in NMC configuration.

 

3. PowerChute starts the operating system shutdown sequence.

 

4. After a 70 second delay the operating system starts to shut down.

Is this 70 second delay hard-coded or configurable?

 

5. The outlet group will turn off after the Power Off Delay configured on the NMC Outlet Group configuration page has elapsed.

If this is correct, then the NMC User Guide falsely says: "Use the sequencing options to define how the UPS will respond to user-issued commands" because the turn off is not issued by a user but by PowerChute.

 

Can anyone clarify these details, please?

-- rpr.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore