error in ATS ap7723

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • error in ATS ap7723
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 07:06 AM . Last Modified: ‎2024-03-04 11:03 PM

0 Likes
6
3395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:06 AM . Last Modified: ‎2024-03-04 11:03 PM

error in ATS ap7723

hi wish for you a good day,

i use ATS ap7723 , i put two source in it , 

i cant see the LED of source ( A ) as show in attached picture ,

i checked the source A by voltmeter from connector it's working but in screen doesn't work,

I've a power down in all racks suddenly every a couple of days ,

consider that Previous IT didn't configure management when they install it the ATS , so i couldn't have any report from it ,

i try to configure it but when it search for ATS network i couldn't find the ATS in serach , you recommend to reset it from the reset bottom for faster search but i cant have a risk down the rack to configure management.

i need to solve the issue of configure management in safe mode without any outage plus i'm seeking for your support and recommend for the issue of source A asap.

pAH4Qv8y3m78bOvtTjim1g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegpAH4Qv8y3m78bOvtTjim1g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7723
  • apc
  • ats
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
3396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

I also have ATS AP7723 can u guys any idea how it works when process switching when source A down then Source B available automaticly and if Source A up again is the main source back to A again? 

thx b4

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-01 07:06 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
3396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:06 AM . Last Modified: ‎2024-03-04 11:02 PM

I would expect to see a green LED next to the "Input A" in your picture if the transfer switch was actually receiving power. If you have the serial console cable (normally 940-0144A) you can connect to the ATS serial console. From there you can see what the ATS thinks it is seeing on its inputs. For example, on an ATS with both inputs connected:

------- ATS Status ------------------------------------------------------------

Source A selected, Switchover Possible

Selected Source : Source A

Preferred Source : Source A

Switch Status : OK

Front Panel : Unlocked

Source A : Selected

Source B : OK

Phase Sync : In sync

Voltage Out : ON

Source A 24V Power Supply : OK

Source B 24V Power Supply : OK

+12V Power Supply : OK

-12V Power Supply : OK

5V Power Supply : OK

 

On an ATS with one source disconnected:

------- ATS Status -------------------------------------- crit: 1 warn: 0 -----

Source A selected, Switchover Not Possible

Selected Source : Source A

Preferred Source : Source B

Switch Status : FAIL

Front Panel : Unlocked

Source A : Selected

Source B : Not Ok

Phase Sync : Out of sync

Voltage Out : ON

Source A 24V Power Supply : OK

Source B 24V Power Supply : OK

+12V Power Supply : OK

-12V Power Supply : OK

5V Power Supply : OK

 

After looking at the ATS status, if it also says that source A is not OK, then you will need to further investigate the power going into the ATS (at the outlet) and if that is OK, you will need to replace the ATS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:06 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
3395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:06 AM . Last Modified: ‎2024-03-04 11:02 PM

I experienced the same issue with an AP7723 and I'm afraid your ATS will need to be replaced. The defect occurred during commissioning/testing of the new ATS whilst manually switching between 2 UPS input supplies (2 x SURT2000). One UPS generated an 'over-voltage' error and was also destroyed. Trouble is, I don't know if the ATS destroyed the UPS or the other way-round. 

Having replaced both the UPS and APS, I then attached an earth bond to the chassis of the ATS. I then continually repeated the ATS input selection testing and the install worked seamlessly as designed.

I have no idea if I was just unlucky with the first failure, or if the addition of an earth bond made any difference in terms of voltage suppression. I'll raise a separate question on here to try and get some answers.

  • Tags:
  • ap7723
  • ats
  • automatic
  • bond
  • earth
  • switch
  • transfer
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
3397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

I also have ATS AP7723 can u guys any idea how it works when process switching when source A down then Source B available automaticly and if Source A up again is the main source back to A again? 

thx b4

Reply

Link copied. Please paste this link to share this article on your social media post.

B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
3395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

Hello,

By default, an AP7723 is configured to have Source A as the "preferred" source. If this setting is not changed, then the ATS will use Source A as the primary source. If A becomes unavailable, the ATS will switch to B, and will switch back to A after it has been available for ~30 seconds.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
3395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

We had this exact same problem.  After opening 4 extra NEW boxes, we finally logged into the device and manually set the input power.  By default it was 230, and we use 208.  It was just enough for one side not to function.  After making the change, both LED's came alive, and all is good following testing.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
3396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:07 AM . Last Modified: ‎2024-03-04 11:02 PM

Sorry for the frustration David. I know it may not help AP7723 users today and in the past but for our future generation of AP44XX series Rack ATS that were just recently released, we have now separated the 208V and 230V models into separate models/part numbers for customers to order and avoid this problem, based on the scenario you just explained. 

Thus, moving forward, if you want 208V and used to buy AP7723, you can now order AP4434 which is set to 208V direct from the factory. If you needed 230V, AP4423 is what you should use. We have done the same for AP7721 which now is replaced by AP4421 or AP4433 depending on if you need 230V or 208V respectively.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of