dla1500RM2u cycles between "replace battery" error and fully-charged state

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • dla1500RM2u cycles between "replace battery" error and fully-charged state
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
4
912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

dla1500RM2u cycles between "replace battery" error and fully-charged state

Hello community,

I have a dla1500rm2u connected to one of our school's servers. I installed a new set of batteries about 2 months ago and has been working fine for the most part. I replaced each of the internal 4 lead-acid batteries separately, not the entire unit.

However, within the past 3 or so weeks, the bad battery/disconnected battery light has been blinking red and beeping continuously. And by continuously, I mean it'll do so for a few hours in the morning, and then be fine (show full green bars on the battery LEDs) the rest of the day. It will beep for an entire day, and be OK the next. It seems random.

I've done hard resets and unplugged and re-plugged all computers a few times as well as the battery connector. No change. Just now I disconnected and reconnected the battery to the unit and the full green bars showed for about 1 minute before going back to "disconnected".

I can post pictures on the batteries and wiring if necessary, but if something was significantly wrong there, I don't know why it worked so well for the first month or so.

What could be the problem and how could I fix it?

Many thanks,

-Shaun

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

Hi Shaun,

Can you clarify - did you replace just the APC Replacement Battery Cartridge or are you saying you took the battery module out and replaced the four batteries in the tray with 3rd party batteries (and have to wire them)? Can you measure the DC voltage from the battery connector or at least view it through PowerChute or a Network Management Card?

The flashing replace battery LED indicates a disconnected (or not detected battery) versus a battery needing to be replaced. This tells me the the battery is maybe going down to a lower voltage where the UPS cannot even see it.

If it is an APC battery, it'd have a serial number/date code on it and technically, we can only support this if you replaced this with a genuine APC battery but if its a third party battery, they also might have a date code that we could verify or figure out how to read by the manufacturer's website.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

SUA1500RM2U, the APC equivalent to DLA1500RM2U, indicates it uses RBC24 which are batteries that come pre-wired in the tray that you just slide in and connect a single connector to. Can I ask why you did not purchase an RBC24 or is that what you did?

Were you able to measure the voltage on the batteries in addition to the resistance? Or in PowerChute data log, does it have the history of the battery voltage that it reports from the UPS?

I am thinking the voltage is dropping below a certain point which I would think indicates a problem with these batteries (maybe that was there since manufacturing) but I am just guessing at this point until I see the voltage.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

Shaunk,

When you re and re'ed the batteries in the tray did you re-tighten every last one of the 1/4" faston terminals ? (via careful crimping with pliers). If you didn't , all it takes is one intermittent connection and the ups will either not see the full capacity of the tray, or be unable to charge all the batteries fully and lead to deterioration of cells and charge levels, and if in conjunction with this the UPS internal battery constant has drifted badly over time, it may not see the batteries at all per Angela's comment. Also, if you used 7.2 Ah batteries instead of the 9.0 Ah cells you may experience runtime and capacity issues over time. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

Hello community,

I have a dla1500rm2u connected to one of our school's servers. I installed a new set of batteries about 2 months ago and has been working fine for the most part. I replaced each of the internal 4 lead-acid batteries separately, not the entire unit.

However, within the past 3 or so weeks, the bad battery/disconnected battery light has been blinking red and beeping continuously. And by continuously, I mean it'll do so for a few hours in the morning, and then be fine (show full green bars on the battery LEDs) the rest of the day. It will beep for an entire day, and be OK the next. It seems random.

I've done hard resets and unplugged and re-plugged all computers a few times as well as the battery connector. No change. Just now I disconnected and reconnected the battery to the unit and the full green bars showed for about 1 minute before going back to "disconnected".

I can post pictures on the batteries and wiring if necessary, but if something was significantly wrong there, I don't know why it worked so well for the first month or so.

What could be the problem and how could I fix it?

Many thanks,

-Shaun

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

Hi Shaun,

Can you clarify - did you replace just the APC Replacement Battery Cartridge or are you saying you took the battery module out and replaced the four batteries in the tray with 3rd party batteries (and have to wire them)? Can you measure the DC voltage from the battery connector or at least view it through PowerChute or a Network Management Card?

The flashing replace battery LED indicates a disconnected (or not detected battery) versus a battery needing to be replaced. This tells me the the battery is maybe going down to a lower voltage where the UPS cannot even see it.

If it is an APC battery, it'd have a serial number/date code on it and technically, we can only support this if you replaced this with a genuine APC battery but if its a third party battery, they also might have a date code that we could verify or figure out how to read by the manufacturer's website.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of