Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84422members
353606posts

ap7723 snmp Monitoring current load

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
dalbjerg_apc
Crewman
Crewman
0 Likes
2
338

ap7723 snmp Monitoring current load

This was originally posted on APC forums on 4/21/2017


Hi

I have googled, to try find out what OID, i should use, to monitoring a AP7723 Current load.-
In the web interface i can see the load is now 5AMP, but witch OID in SNMP should i used to see this number to SNMP?

Hope someone can help me.
Thx.

Regards Kenneth Dalbjerg

Tags (4)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
338

Re: ap7723 snmp Monitoring current load

This reply was originally posted by Angela on APC forums on 4/24/2017


Hi Kenneth,

Please look at the following OID in the APC PowerNet MIB: .1.3.6.1.4.1.318.1.1.8.5.4.3.1.4 (.iso.org.dod.internet.private.enterprises.apc.products.hardware.automaticTransferSwitch.atsStatus.atsStatusOutput.atsOutputPhaseTable.atsOutputPhaseEntry.atsOutputCurrent)

I used a MIB browser which is helpful to see all of the OIDs available, especially if you may be interested in other OIDs like the output VA.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
339

Re: ap7723 snmp Monitoring current load

This reply was originally posted by Angela on APC forums on 4/24/2017


Hi Kenneth,

Please look at the following OID in the APC PowerNet MIB: .1.3.6.1.4.1.318.1.1.8.5.4.3.1.4 (.iso.org.dod.internet.private.enterprises.apc.products.hardware.automaticTransferSwitch.atsStatus.atsStatusOutput.atsOutputPhaseTable.atsOutputPhaseEntry.atsOutputCurrent)

I used a MIB browser which is helpful to see all of the OIDs available, especially if you may be interested in other OIDs like the output VA.

dalbjerg_apc
Crewman
Crewman
0 Likes
0
338

Re: ap7723 snmp Monitoring current load

This was originally posted on APC forums on 4/24/2017


Thank you. I also think it was this one, but it response, was ten time high, than it should be.
Just google it, and it says it gives the status in milli amps 🙂

Again thanks for you help