Hi again,
I have another question (or two) about the network power strips. We would like to be able to run a script that power cycles the outlets. Any advice or hints on how to do this?
I was also wondering if there was a way to shutdown servers connected to the outlets, other than just cutting power. Is there any way to start a shutdown. I see that APC makes Powerchute software. Would that work?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:33 AM . Last Modified: 2024-03-18 11:09 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:33 AM . Last Modified: 2024-03-18 11:09 PM
Hi again,
I have another question (or two) about the network power strips. We would like to be able to run a script that power cycles the outlets. Any advice or hints on how to do this?
I was also wondering if there was a way to shutdown servers connected to the outlets, other than just cutting power. Is there any way to start a shutdown. I see that APC makes Powerchute software. Would that work?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:33 AM . Last Modified: 2024-03-18 11:09 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:33 AM . Last Modified: 2024-03-18 11:09 PM
Hi Smalls,
In regards to the scripting question, as long as your PDU has firmware 2.70 or higher, you can use the command line interface built into the rPDU. To access the command line interface, when you log into the PDU via Hyperterminal/Telnet/SSH, use your regular username (apc is default). For the password, use your password, insert a space, and type "-c" (apc
Let us know if you have any additional questions.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:33 AM . Last Modified: 2024-03-18 11:09 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:33 AM . Last Modified: 2024-03-18 11:09 PM
Hi again,
I have another question (or two) about the network power strips. We would like to be able to run a script that power cycles the outlets. Any advice or hints on how to do this?
I was also wondering if there was a way to shutdown servers connected to the outlets, other than just cutting power. Is there any way to start a shutdown. I see that APC makes Powerchute software. Would that work?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.