Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Where to configure the Agent v9.1.0-614 to cancel shutdown if power is restored?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Where to configure the Agent v9.1.0-614 to cancel shutdown if power is restored?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:24 AM

0 Likes
17
806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

Where to configure the Agent v9.1.0-614 to cancel shutdown if power is restored?

This was originally posted on APC forums on 6/5/2013


Hi!

I havea Linux serverina Smart-UPS (SUA1000BR).

I installedandconfigured successfully the Agentv9.1.0-614 soif the power failsfor 3 minutesis giventoshutdowntheserver:

Events / Actions/Power failed/
Commandfile execution: √ Enable

File name😕opt /APC/........./default.sh
Duration: 3 minutes

√InitiateShutdown Sequence

I noticed thatwhen the power isrestored after 2 minutes,theshutdownis not automaticallycanceled.
      

Where to configure the Agent v9.1.0-614 to cancel shutdown if power is restored?

Thank you.

Priscila.        

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This was originally posted on APC forums on 6/13/2013


ApologiesBill, I had not noticedthe "Show Advanced Items."

ConfiguringPower Failureparametervia PowerChuteServer/Consoleautomaticallysawthat madenew changesin otherparametersin the Agent. I keptthese changesand nowyes, UPS is functioning asneed.

Againgratefulfor the guidance.

Best Regards,

Priscila.

See Answer In Context

Reply
Share
Replies 17
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This reply was originally posted by Angela on APC forums on 6/5/2013


Unfortunately, there is no way to cancel the shutdown once its in progress. The UPS will also be in a "reboot" cycle which needs to complete by turning off (and any PCNS clients) and then turning back on when it sees AC power is back - which in this situation would happen immediately almost since the power failure is no longer in progress.

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This was originally posted on APC forums on 6/5/2013


Hi Priscila,

I agree with Angela. Once a shutdown starts, it must run to completion because attached computers are in the process of shutting down.

In your question, you've stated that shutdown starts after 3 minutes of power failure. You also say that shutdown isn't cancelled if power returns in 2 minutes. Is that 2 minutes from when the power failure began? In that case, the shutdown won't occur unless you have some other condition that starts the shutdown earlier. Or is that 2 minutes after the shutdown started (5 minutes from when the power failure began)?

Reply
Share
nael_apc
Lieutenant JG nael_apc
Lieutenant JG

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This was originally posted on APC forums on 6/6/2013


Hi

Yes. there is no way to cancel the shutdown once its in progress

Reply
Share
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This was originally posted on APC forums on 6/6/2013


Hi to all!
Thanks for the responses.

Look what is happening here:
I am simulating a power failure.
Programmed to start the shutdown 3 minutes after the power failure.

Reinstate power after 2 minutes of the failure (missing even 1 minute to start the shutdown) but still after 1 minute, the shutdown is initiated.

Actually I do not want to stop the shutdown but cancel the start of the shutdown.

Grateful for more help.

Priscila.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This reply was originally posted by Bill on APC forums on 6/6/2013


Priscila,

The way you have the configuration set up now once the power fails the shutdown starts and cannot be cancelled. How it works is, UPS recognizes the power failure and reports that to PCBE.  Since you have configured the event Power Failed to shutdown but have also configured a command file to run with a duration of 3 minutes PCBE start the command file execution and starts a count down for the shutdown. When the 3 minutes elapse the OS shutdown command is initiated even if the power has been restored.

There is no cancel button at this time. I will add it as an enhancement request for future versions.

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This was originally posted on APC forums on 6/6/2013


prisantos wrote:

Look what is happening here:
I am simulating a power failure.
Programmed to start the shutdown 3 minutes after the power failure.

Reinstate power after 2 minutes of the failure (missing even 1 minute to start the shutdown) but still after 1 minute, the shutdown is initiated.

Actually I do not want to stop the shutdown but cancel the start of the shutdown.

Okay, so if the power failure lasts longer than 1 minute, the UPS initiates a shutdown despite the fact you've set it to shutdown only after 3 minutes?

Bill suggests that perhaps the 3 minute duration you've set is the "script execution delay" rather than time on battery?

If that's not the case, there's probably another shutdown condition that triggers first. For example, the NMC will start a shutdown if the runtime available (amount of time the UPS can provide power) drops below the "low battery duration". The best way to check this out is to copy the event logs from PCNS and the NMC showing the shutdown. You can attach them as files on the forum.

Reply
Share
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This was originally posted on APC forums on 6/6/2013


Bill,

I'm so dissatisfiedwithwhat you are writingI thinkI'm notmaking meunderstand.

I seethat thereare manyparametersin theAgentto be configuredas:

Powerrestored, Shutdowncancelled, Invalid shutdowndelay.........

Please, Is there noparameterthatdo whatdo I need?

Need:Just giveshutdowntheserver ifthere is a power failure for 3consecutive minutes.

           If the power failsfrom 1 secondto179 secondsnoshutdown.

Grateful formore help.

Priscila.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This reply was originally posted by Bill on APC forums on 6/7/2013


Priscila,

After re-reading your post I noticed something that does not make sense. You listed the Smart-UPS as SUA1000BR. The SUA1000BR would not use Agent version 9.1.0. It should be using Agent version 9.0.2. So before going forward please verify the exact model of the Smart-UPS and the version of the PowerChute Agent.

Reply
Share
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:24 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:24 AM

This was originally posted on APC forums on 6/7/2013


Hi Bill.

Smart-UPS 1000 (SUA1000BR).

Inmy variousattempts to work asaccurate (and I think that is the correct wayfor a programthat managesa UPS work) I had alreadyuninstalled theAgent9.1.0-614.i386 andinstalledthe9.0.2-614. i386.

Sonow I'mwith PowerChute Agent9.0.2-614and the problem persists .

Grateful formore help.

Priscila.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This reply was originally posted by Bill on APC forums on 6/7/2013


Thanks for confirming the version.

Did you install the Server and Console? If you did then to shut the OS down after being on battery for 3 minutes you need double click on the the device in the console Like I have highlighted below

1229_pastedImage_0.png

From there be sure that Show advanced items is check at the bottom of the page.

1230_pastedImage_1.png

Once that is done you should select Server Shutdown - Power Failure

1231_pastedImage_2.png

This is where you can configure the software to shut the system down after being on battery for 3 minutes

If in that 3 minutes the power is restored then the OS will not shutdown.

You should then open the web interface you have been using and deselect shutdown on power failed.

Reply
Share
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This was originally posted on APC forums on 6/7/2013


Bill,

No.I am settingthe Agentdirectly frommy Linux servervia browser. The interfaceis another.

OnServerShutdown/ShutdownSettings/PowerSettingsReturnis:

- EnableOSReboot

- TurnonUPSbatterycapacity

- UPSturnondelay

Where isthe parameterthat you areasking todeselecttheintefacethat I am using?

There: Events /Actions/Power restored/

I got nothingbutchangingthis parameter.

Grateful formore help.

Priscila.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This reply was originally posted by Bill on APC forums on 6/10/2013


Priscila,

With that OS and a SUA model Smart-UPS your option are

Install the Server and Console on a Windows system and have the Agent running on the Linux system monitored by that system.

Change the shutdown configuration via the web interface to shut the OS down by the Low Battery Signal time or configure Runtime Remaining Threshold (these can be found under Server Shutdown - Shutdown Settings).

Upgrade to a SMT model Smart-UPS.

Reply
Share
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This was originally posted on APC forums on 6/10/2013


Bill,

I'mwithPowerChuteAgentv9.0(pbeagent-9.0.1-614.i386.rpm) installed on the Linux server.

I need thePowerChuteBusiness Edition(Server andConsole) v9.0. Correct ?

The APC websiteonly foundversion 9.1. Inarchived versions ofsoftwaredoes not have.
Where do I findthe version9.0- 5 Node (SFPCBE90 - free download) for WindowsXP?

Grateful formore help.

Priscila.

Reply
Share
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This was originally posted on APC forums on 6/11/2013


Bill,

Regrettably inform that after following your directions, I have not found the Power Failure parameter in version 9.0 of PowerChute Business Edition available for you.
From what I observed the Power Failure parameter (under Server Shutdown - Shutdown Settings) is only available in version 9.1.

As the agent 9.1 does not work on Linux, I think it will not be able to manage the UPS as need.

Always used with complete success, the UPC UPS Daemon Linux (apcupsd) to manage APC UPS, but now there is a incompatibility protocol of
with the new APC UPSs (a new communication protocol called "Microlink") with apcupsd. So my interest  PowerChute ....


Unfortunately I can not have new APC products on my Linux servers.


Thanks to all!

Best Regards,
Priscila

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This reply was originally posted by Bill on APC forums on 6/10/2013


Priscila,

I just sent you a like to where you can download PCBE 9.0.1 for Windows

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This reply was originally posted by Bill on APC forums on 6/11/2013


Priscila,

Did you click on Show Advanced Items? When you select show advanced items the setting you are looking for will be available for your SUA model Smart-UPS. BTW,  SUA model Smart-UPS are not Microlink they are UPSlink. If you are using a Microlink Smart-UPS then you should install PowerChute Business Edition 9.1 and use the web interface. You can then adjust the setting you would like through that.

Reply
Share
prisantos_apc
Crewman prisantos_apc
Crewman

Posted: ‎2021-07-01 03:25 AM

0 Likes
0
805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 03:25 AM

This was originally posted on APC forums on 6/13/2013


ApologiesBill, I had not noticedthe "Show Advanced Items."

ConfiguringPower Failureparametervia PowerChuteServer/Consoleautomaticallysawthat madenew changesin otherparametersin the Agent. I keptthese changesand nowyes, UPS is functioning asneed.

Againgratefulfor the guidance.

Best Regards,

Priscila.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc