Posted: 2023-06-02 04:13 AM
I'm struggling to find a compatible serial cable for my APC 7722 ATS - the device has a serial port at the front and I'm trying to get to the NMC which is AP9617 which only has 10/100 Ethernet and a reset button.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-19 03:31 AM
Anyone?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-08-23 05:16 AM
Hi AdrianK_apc,
You may want to check the FAQ below and look at the table of the cables applicable.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-08-31 08:27 AM
Odds are good you need APC PN 940-0024C
That's what we used for Smart-UPS when we had AP9617 NMC's