Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What is the maximum load for an AP8941

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What is the maximum load for an AP8941
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:10 AM

0 Likes
2
2323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:10 AM

What is the maximum load for an AP8941

Hi,

The AP8941 is listed on the APC website as "Rack PDU 2G, Switched, ZeroU, 30A, 200/208V, (21) C13 & (3) C19"

However, when you log in to the device it has a rating of 24A.

Does anyone know what rating the two breakers are on the PDU and whether it is safe to push the loaf up to 30A?

Thanks,

Glenn

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:10 AM

0 Likes
0
2323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:10 AM

Hello,

The AP8941 is a 30A unit, meaning it has a 30A plug on it. Its rating is 80% of that (for the USA) which is 24A. I believe it has two banks on it with a maximum rating of 20A, with a rating of 16A. This PDU should have a 30A breaker feeding it and will trip at 30A. The bank breakers will actually trip at 20A since that is their max rating.

Depending on the region though, they might not go by the 80% rule that we have here in the USA with National Electrical Code which we have here for UPS, but it applies to PDU too -> Why is my APC by Schneider Electric UPS derated to 80% of the circuit's total capacity? | FAQs | Sch...

With all of that said, since all regions don't go by this 80% rule, what they did is put the 20A banks with a threshold range from 0-22A so that users could disable it ultimately if they wanted and a little bit to account for some slight inaccuracy measurement scenarios.

Technically, you should not load this PDU over 24A total, or 16A for each bank and if you do, it should not last for more than 3 hours. Anything that runs over 3 hours should be sized per 80% rule and ultimately, you should have larger than a 30A breaker feeding the PDU. All of the internal components are rated for 30A though.

Here is some information i have saved from our compliance team on the topic:

First, let me state that as far as rack PDUs are concerned, there is no such thing as "UL derating." While a product may have a 30 amp plug and 30 amp circuit breakers, the product rating is 24 A - period. There is no allowance for exceeding this current.

Any concept of derating in the US and Canada comes from the US NEC and the Canadian CEC, stating that a circuit breaker cannot be loaded to more that 80% of its rating for continuous loads. By definition, IT equipment is considered a continuous load. Below from the UL requirements for circuit breakers.  

"Unless otherwise marked, circuit breakers should not be loaded to exceed 80% of their current rating, where in normal operation the load will continue for three hours or more."

They are going to change the breaker thresholds again because of confusion users have had and my own original confusion too. AP8941 happens to be sold in multiple regions like NAM and Japan.

Hope this helps. Let me know if you have other questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:10 AM

0 Likes
0
2324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:10 AM

Hello,

The AP8941 is a 30A unit, meaning it has a 30A plug on it. Its rating is 80% of that (for the USA) which is 24A. I believe it has two banks on it with a maximum rating of 20A, with a rating of 16A. This PDU should have a 30A breaker feeding it and will trip at 30A. The bank breakers will actually trip at 20A since that is their max rating.

Depending on the region though, they might not go by the 80% rule that we have here in the USA with National Electrical Code which we have here for UPS, but it applies to PDU too -> Why is my APC by Schneider Electric UPS derated to 80% of the circuit's total capacity? | FAQs | Sch...

With all of that said, since all regions don't go by this 80% rule, what they did is put the 20A banks with a threshold range from 0-22A so that users could disable it ultimately if they wanted and a little bit to account for some slight inaccuracy measurement scenarios.

Technically, you should not load this PDU over 24A total, or 16A for each bank and if you do, it should not last for more than 3 hours. Anything that runs over 3 hours should be sized per 80% rule and ultimately, you should have larger than a 30A breaker feeding the PDU. All of the internal components are rated for 30A though.

Here is some information i have saved from our compliance team on the topic:

First, let me state that as far as rack PDUs are concerned, there is no such thing as "UL derating." While a product may have a 30 amp plug and 30 amp circuit breakers, the product rating is 24 A - period. There is no allowance for exceeding this current.

Any concept of derating in the US and Canada comes from the US NEC and the Canadian CEC, stating that a circuit breaker cannot be loaded to more that 80% of its rating for continuous loads. By definition, IT equipment is considered a continuous load. Below from the UL requirements for circuit breakers.  

"Unless otherwise marked, circuit breakers should not be loaded to exceed 80% of their current rating, where in normal operation the load will continue for three hours or more."

They are going to change the breaker thresholds again because of confusion users have had and my own original confusion too. AP8941 happens to be sold in multiple regions like NAM and Japan.

Hope this helps. Let me know if you have other questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:04 AM . Last Modified: ‎2024-03-18 12:10 AM

0 Likes
0
2322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:04 AM . Last Modified: ‎2024-03-18 12:10 AM

That's very helpful! Thank you Angela

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore