APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 05:32 AM . Last Modified: 2024-03-18 03:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:32 AM . Last Modified: 2024-03-18 03:18 AM
We suffered a power loss at one of our data centres over the weekend. Strangely, the logs for the A feed showed a cold start on the power rails, but the B side logs all showed warmstarts. I'm wondering what the difference is, and why the rails would choose to spontaneously warmstart?
Any help greatly appreciated.
Bernie
"B" Feed Log
28.11.2010 08:27:16 Switched Rack PDU: Near overload cleared on bank 1.
28.11.2010 08:16:35 Switched Rack PDU: Near overload on bank 1.
28.11.2010 08:16:33 Switched Rack PDU: Communications established.
28.11.2010 08:16:25 System: Network service started. System IP is (Address) from manually configured settings.
28.11.2010 08:16:25 System: Warmstart.
"A" Feed log
28.11.2010 08:28:21 Switched Rack PDU: Communications established.
28.11.2010 08:28:12 System: Network service started. System IP is (Address) from manually configured settings.
28.11.2010 08:28:12 System: Coldstart
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:32 AM . Last Modified: 2024-03-18 03:18 AM
hi, you can reference [this knowledgebase article|http://nam-en.apc.com/app/answers/detail/a_id/2572/] on the subject.
in summary, a coldstart indicates the power was lost to the network management card and it rebooted where as a warmstart is just a reboot without losing power, much like a PC can be power cycled or "soft rebooted" with a restart command.
what were the switched rack PDUs plugged into? a UPS? ATS? that may help us figure out what happened. do you have any info from the data log at the same time?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:32 AM . Last Modified: 2024-03-18 03:18 AM
hi, you can reference [this knowledgebase article|http://nam-en.apc.com/app/answers/detail/a_id/2572/] on the subject.
in summary, a coldstart indicates the power was lost to the network management card and it rebooted where as a warmstart is just a reboot without losing power, much like a PC can be power cycled or "soft rebooted" with a restart command.
what were the switched rack PDUs plugged into? a UPS? ATS? that may help us figure out what happened. do you have any info from the data log at the same time?