Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Voltages b/w Neutral & Ground on Battery Operations
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2510:51 PM. Last Modified: 2024-03-1903:25 AM
Voltages b/w Neutral & Ground on Battery Operations
Dear Team,
Further to the Knowledge Base FA156549, colud you please confirm if it only implies to SMART UPS ONLINE & BACK UPS or the same voltages will be recorded in other UPSs at large and GALAXY 300 in particular.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2510:51 PM. Last Modified: 2024-03-1903:25 AM
I believe the article was created by our Back UPS and Smart UPS team. I checked into this with someone in our EMEA support for 3 phase UPSs. I don't know much on 3 phase here personally but here is what I was told:
Normally all the three phase UPS systems have a Neutral that goes straight through. It is mentioned that the Neutral is bonded to ground at the source. However that is not always the case. In EMEA we have various grounding configurations e.g TN, TT or IT, depending on country / region. The Neutral is bonded to ground at the entry to the building in a TN-S or TN-CS Network. In many countries, mainly in Southern Europe a TT Network is used. Here the Fault current goes through the earth via an earth spike and large RCD's (GFI's) must be used and if tripped the neutral is broken. Depending on the impedance of the Earth Spike, there may be a voltage between Ground and Neutral.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2510:51 PM. Last Modified: 2024-03-1903:25 AM
I believe the article was created by our Back UPS and Smart UPS team. I checked into this with someone in our EMEA support for 3 phase UPSs. I don't know much on 3 phase here personally but here is what I was told:
Normally all the three phase UPS systems have a Neutral that goes straight through. It is mentioned that the Neutral is bonded to ground at the source. However that is not always the case. In EMEA we have various grounding configurations e.g TN, TT or IT, depending on country / region. The Neutral is bonded to ground at the entry to the building in a TN-S or TN-CS Network. In many countries, mainly in Southern Europe a TT Network is used. Here the Fault current goes through the earth via an earth spike and large RCD's (GFI's) must be used and if tripped the neutral is broken. Depending on the impedance of the Earth Spike, there may be a voltage between Ground and Neutral.