Using Network Monitoring Software with APC UPS BX1200MI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Using Network Monitoring Software with APC UPS BX1200MI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
aviado
aviado
Cadet

Posted: ‎2023-10-03 10:59 PM

0 Likes
3
4229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-03 10:59 PM

Using Network Monitoring Software with APC UPS BX1200MI

I currently have an APC UPS model BX1200MI connected to my PC via USB (we have several APC UPS units) . I have successfully installed and configured the PowerChute Personal Edition v3.1 software, and it's working fine for monitoring my UPS locally.

However, I am wondering if there's a way to utilize network monitoring software instead of PowerChute Personal Edition v3.1. Specifically, I would like to monitor my UPS from our organization's monitoring server (Host Monitor) directly.

Is there any compatible network monitoring software that can be used with the APC BX1200MI? I am looking for a solution that allows remote monitoring and management of the UPS unit over the network, preferably one that can integrate with our existing monitoring infrastructure.

Thank you in advance for your assistance!

Best regards,

Aviad

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
dpierce4776
Lt. Commander dpierce4776
Lt. Commander

Posted: ‎2023-10-04 08:46 PM

0 Likes
0
4205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-04 08:46 PM

You would need a UPS that has a monitoring card. The APC BX1200MI is only connected though USB. If your other UPSs have a networking monitoring card such as the APC AP9640 then yes you can monitor all of them. APC has software called POC software called Datacenter Expert at https://dcimsupport.ecostruxureit.com/hc/en-us/articles/360039289653-Data-Center-Expert-Virtual-Appl...

If you want to take a look at it.
As far as "integrating with your existing monitoring infrastructure." That would depend on your current monitoring infrastructure. But Struxureware does a really good job at alerting, FW upgrades, reporting, and the like as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
Lt. Commander dpierce4776
Lt. Commander

Posted: ‎2023-10-04 08:49 PM

0 Likes
0
4205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-04 08:49 PM

Check out https://dcimsupport.ecostruxureit.com/hc/en-us/articles/360039289653-Data-Center-Expert-Virtual-Appl...

But this only works if your devices have a network monitoring care such as the AP9640

Reply

Link copied. Please paste this link to share this article on your social media post.

Morgan_D
Crewman Morgan_D Crewman
Crewman

Posted: ‎2023-10-08 06:06 PM

0 Likes
0
4187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-08 06:06 PM

Indeed you need a network management card, to monitor or control it remotely through your network.
Yet for Back UPS, in the past some users used apcupsd (opensource daemon) to connect their UPS with USB on their computer, and then script the host monitor. But it still mean you need to go through the computer with the UPS on USB... and this can be a major flaw.

 

I hope you have Smart UPS for the rest of your infra, then you can use the network function thanks to network management cards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore