Upgrading firmware on AP8981 (Switched Rack PDU)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Upgrading firmware on AP8981 (Switched Rack PDU)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
skendric
Crewman skendric
Crewman

Posted: ‎2022-06-24 12:19 PM

0 Likes
2
2437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-24 12:19 PM

Upgrading firmware on AP8981 (Switched Rack PDU)

BRIEF

I am upgrading APC AP8981 from AOS/RPDU2G 6.8.x and 6.9.x to 7.0.4.  Generally, works fine ... but for (2) units, they revert to the previous firmware version, after the process completes.  Tips on trouble-shooting?

 

The NMC Firmware Update Utility claims that the process has completed successfully.  And for most units, it has.  But for a couple of units, while the NMC Utility claims success:

 

[06/24/2022 09:25:52] NMC Firmware Update Utility v1.0.3 initialized.
[06/24/2022 09:26:06] Downloading and verifying configuration file from dc-705-pdu, please wait...
[06/24/2022 09:26:27] Uploading firmware file 1 of 3: Boot Monitor to dc-705-pdu, please wait...
[06/24/2022 09:26:39] Waiting for the network interface on dc-705-pdu to restart, please wait...
[06/24/2022 09:27:05] Uploading firmware file 2 of 3: APC Operating System to dc-705-pdu, please wait...
[06/24/2022 09:28:38] Waiting for the network interface on dc-705-pdu to restart, please wait...
[06/24/2022 09:29:59] Uploading firmware file 3 of 3: Application to dc-705-pdu, please wait...
[06/24/2022 09:31:22] Waiting for the network interface on dc-705-pdu to restart, please wait...
[06/24/2022 09:31:54] Entire update process has been completed.

 

Nevertheless, when I log back in, I see that while bootmon has been upgraded, that AOS and RPU2G remain back on the previous 6.8.2/6.8.0 versions

 

I have tried performing the process manually, i.e.

linux>:$ ftp dc-705-pdu

Connected to dc-705-pdu.
220 AP8981 Network Management Card AOS v6.8.2 FTP server ready.
Name (dc-705-pdu:tech): apc
331 User name okay, need password.
Password:
230 User logged in, proceed.
ftp> bin
200 TYPE Command okay.
ftp> hash
Hash mark printing on (1024 bytes/hash mark).
ftp> put apc_hw05_aos_704.bin
local: apc_hw05_aos_704.bin remote: apc_hw05_aos_704.bin
200 PORT Command okay.
150 File status okay; about to open data connection.
################################################################################

[...]

##########
226 Closing data connection.
3123200 bytes sent in 51.32 secs (59.4326 kB/s)
ftp>

 

Wait for the NMC to reboot, then ftp back in ... notice how the AOS upgrade has been successful (v7.0.4)

stuartk@indra:/tftpboot/APC$ ftp dc-701-pdu
Connected to dc-701-pdu.
220 AP8981 Network Management Card AOS v7.0.4 FTP server ready.
Name (dc-701-pdu:stuartk): apc
331 User name okay, need password.
Password:
230 User logged in, proceed.
ftp> bin
200 TYPE Command okay.
ftp> hash
Hash mark printing on (1024 bytes/hash mark).
ftp> put apc_hw05_rpdu2g_706.bin
local: apc_hw05_rpdu2g_706.bin remote: apc_hw05_rpdu2g_706.bin
200 PORT Command okay.
150 File status okay; about to open data connection.
################################################################################

[...]

########
226 Closing data connection.
2712100 bytes sent in 45.63 secs (58.0456 kB/s)
ftp>

 

But ... when log back in ... the device has reverted to the previous firmware

linux> ssh dc-705-pdu -l apc
apc@dc-705-pdu's password:


Schneider Electric Network Management Card AOS v6.9.6
(c) Copyright 2020 All Rights Reserved RPDU 2g APP v6.9.6

[...]

 

 

TROUBLE-SHOOTING

- I have tried resetting the configuration (except for TCIP/IP settings), same behavior

- The Event Log contains no suggestion of problems (records the file transfers but no discussion of an upgrade attempt)

 

 

NEXT STEPS

- Suggestions on how I might trouble-shoot this further?

 

--sk

 

Stuart Kendrick

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
BrandonD
BrandonD
Cadet

Posted: ‎2023-03-22 10:32 AM

0 Likes
1
2156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 10:32 AM

Were you able to solve this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

skendric
Crewman skendric
Crewman

Posted: ‎2023-03-23 02:08 PM

In response to BrandonD
0 Likes
0
2138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-23 02:08 PM

No

 

Actually, the 2nd PDU now claims to be running AOS 1.5.1.1 and rPDU 1.2.0.2 (and BootMon 1.3.6.1) ... which is even more surprising than the previous behavior

 

I haven't figured out a different angle to take on this -- if you have suggestions, do let me know

 

--sk

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore