UPS upstream breaker sizing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS upstream breaker sizing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ethode_apc
Crewman ethode_apc
Crewman

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:22 AM

0 Likes
3
4298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:22 AM

UPS upstream breaker sizing

So we're running into a really interest issue.

1) We have a Symmetra PX 80kw with the 480v PDU (pd80g6fk1)

2) The PDU says 160 amps input

3) Your website says max 135 amps (http://www.apc.com/shop/us/en/products/InfraStruxure-PDU-80kW-480V-208V-W-MBP/P-PD80G6FK1-M)

4) The manual says 150 amp up stream breaker.

All of these amp ratings seem to contradict each other; can someone explain?  Even at a power factor of .80 (assumed) 80kw would need 100kva to service that 80kw which makes sense according to the name plate, but that also means that 120 amps is it's maximum.. None of this makes sense. haha

Thanks in advanced!

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • 100kva
  • 80kw
  • breaker
  • px
  • sizing
  • symmetra
  • ups
  • upstream
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:22 AM

0 Likes
0
4290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:22 AM

Hi,

The transformer in that PDU is a 112.5KW not 100 or 80k and requires the 150A (per notes should be 100% rated 150A or 80% 175A)
kw x 1000 / V x pf x 1.732
112,500 / 480 x .982 x 1.732
112,500 / 816.39 = 138A
138 x 1.25 = 172.5A (closest standard size CB is 150A as to not over size for safety)

The Certified Electrician's Instruction list the breaker at 150A 

http://www.apcmedia.com/salestools/ASTE-6YWKJE/ASTE-6YWKJE_R0_EN.pdf?sdirect=true


Its common that Schneider will use a slightly larger isolation transformer in the PDU products. Over sizing of the input transformer is better than using a K13 rated transformer to handle harmonics. However, the PDU is only rated for 80kW therefore, 150A input CB is required.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:22 AM

0 Likes
0
4291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:22 AM

Hi,

The transformer in that PDU is a 112.5KW not 100 or 80k and requires the 150A (per notes should be 100% rated 150A or 80% 175A)
kw x 1000 / V x pf x 1.732
112,500 / 480 x .982 x 1.732
112,500 / 816.39 = 138A
138 x 1.25 = 172.5A (closest standard size CB is 150A as to not over size for safety)

The Certified Electrician's Instruction list the breaker at 150A 

http://www.apcmedia.com/salestools/ASTE-6YWKJE/ASTE-6YWKJE_R0_EN.pdf?sdirect=true


Its common that Schneider will use a slightly larger isolation transformer in the PDU products. Over sizing of the input transformer is better than using a K13 rated transformer to handle harmonics. However, the PDU is only rated for 80kW therefore, 150A input CB is required.

Reply

Link copied. Please paste this link to share this article on your social media post.

ethode_apc
Crewman ethode_apc
Crewman

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:21 AM

0 Likes
0
4290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:21 AM

Thanks Bill. Down the road we assume that we're putting in a "B" UPS unit and it will be 225kw instead of the 80kw we have now and we will decommission this current UPS and upgrade it as well.

While we're finishing up the panel board, can tell me upstream breaker size we would need to cover a future 225kw UPS?

Thanks!

  • Tags:
  • 225kw
  • pdu
  • symmetra
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

ethode_apc
Crewman ethode_apc
Crewman

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:21 AM

0 Likes
0
4290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:26 AM . Last Modified: ‎2024-03-19 02:21 AM

Was able to get ahold of an APC rep... Wanted to answer this for future readers

A 225kw UPS would windup with a 350amp breaker and 250kw would be 400amp.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of