Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84597members
353862posts

UPS upstream breaker sizing

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
ethode_apc
Crewman
Crewman
0 Likes
3
497

UPS upstream breaker sizing

This was originally posted on APC forums on 5/18/2016


So we're running into a really interest issue.

1) We have a Symmetra PX 80kw with the 480v PDU (pd80g6fk1)

2) The PDU says 160 amps input

3) Your website says max 135 amps (http://www.apc.com/shop/us/en/products/InfraStruxure-PDU-80kW-480V-208V-W-MBP/P-PD80G6FK1-M)

4) The manual says 150 amp up stream breaker.

All of these amp ratings seem to contradict each other; can someone explain?  Even at a power factor of .80 (assumed) 80kw would need 100kva to service that 80kw which makes sense according to the name plate, but that also means that 120 amps is it's maximum.. None of this makes sense. haha

Thanks in advanced!


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
497

Re: UPS upstream breaker sizing

This reply was originally posted by Bill on APC forums on 5/19/2016


Hi,

The transformer in that PDU is a 112.5KW not 100 or 80k and requires the 150A (per notes should be 100% rated 150A or 80% 175A)
kw x 1000 / V x pf x 1.732
112,500 / 480 x .982 x 1.732
112,500 / 816.39 = 138A
138 x 1.25 = 172.5A (closest standard size CB is 150A as to not over size for safety)

The Certified Electrician's Instruction list the breaker at 150A 

http://www.apcmedia.com/salestools/ASTE-6YWKJE/ASTE-6YWKJE_R0_EN.pdf?sdirect=true


Its common that Schneider will use a slightly larger isolation transformer in the PDU products. Over sizing of the input transformer is better than using a K13 rated transformer to handle harmonics. However, the PDU is only rated for 80kW therefore, 150A input CB is required.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
498

Re: UPS upstream breaker sizing

This reply was originally posted by Bill on APC forums on 5/19/2016


Hi,

The transformer in that PDU is a 112.5KW not 100 or 80k and requires the 150A (per notes should be 100% rated 150A or 80% 175A)
kw x 1000 / V x pf x 1.732
112,500 / 480 x .982 x 1.732
112,500 / 816.39 = 138A
138 x 1.25 = 172.5A (closest standard size CB is 150A as to not over size for safety)

The Certified Electrician's Instruction list the breaker at 150A 

http://www.apcmedia.com/salestools/ASTE-6YWKJE/ASTE-6YWKJE_R0_EN.pdf?sdirect=true


Its common that Schneider will use a slightly larger isolation transformer in the PDU products. Over sizing of the input transformer is better than using a K13 rated transformer to handle harmonics. However, the PDU is only rated for 80kW therefore, 150A input CB is required.

ethode_apc
Crewman
Crewman
0 Likes
0
497

Re: UPS upstream breaker sizing

This was originally posted on APC forums on 6/3/2016


Thanks Bill. Down the road we assume that we're putting in a "B" UPS unit and it will be 225kw instead of the 80kw we have now and we will decommission this current UPS and upgrade it as well.

While we're finishing up the panel board, can tell me upstream breaker size we would need to cover a future 225kw UPS?

Thanks!

Tags (4)
ethode_apc
Crewman
Crewman
0 Likes
0
497

Re: UPS upstream breaker sizing

This was originally posted on APC forums on 6/14/2016


Was able to get ahold of an APC rep... Wanted to answer this for future readers

A 225kw UPS would windup with a 350amp breaker and 250kw would be 400amp.