UPS shutdown during self test due to bad battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS shutdown during self test due to bad battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:05 AM . Last Modified: ‎2024-03-12 04:46 AM

0 Likes
1
794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:05 AM . Last Modified: ‎2024-03-12 04:46 AM

UPS shutdown during self test due to bad battery

Is this expected behavior? We buy these to protect our equipment from loss of power, and here we have the UPS is the reason for the loss of power, cutting off power to $100k of attached equipment. In this instance I would have been better off with no UPS at all as power hasn't gone out in this building since the blackout 10 years ago.

I've never had this issue with the other 3000's and 2200's we have here, most of which have had bad battery alerts at some point.

Do I just trash this unit and go with another model or brand? Is this a common occurrence? Our servers are running on redundant UPS's, but that's primarily to avoid prolonged power issues with a single circuit. At this point I'm thinking I'll need a dual input PDU and 2 UPS's as I can't rely on these APC's to stay on if they detect a bad battery.

Model: Smart-UPS 2200 RM

Firmware Revision:     665.6.D

10/15/2013     15:32:07     UPS: The battery is now installed.

10/15/2013     15:31:50     UPS: The battery is not installed properly.

10/15/2013     15:31:16     UPS: The battery is now installed.

10/15/2013     15:30:59     UPS: The battery is not installed properly.

10/15/2013     15:30:42     UPS: The battery is now installed.

10/15/2013     14:55:08     UPS: The output power is turned off.

10/15/2013     04:09:14     System: Set Date or Time.

10/14/2013     04:08:53     System: Set Date or Time.

10/13/2013     04:08:35     System: Set Date or Time.

10/12/2013     04:08:17     System: Set Date or Time.

10/12/2013     02:04:32     UPS: The battery is not installed properly.

10/12/2013     02:04:16     UPS: The battery is now installed.

10/12/2013     02:02:32     UPS: The battery is not installed properly.

10/12/2013     02:02:16     UPS: The battery is now installed.

10/12/2013     02:01:41     UPS: The battery is not installed properly.

10/12/2013     02:01:24     UPS: The battery is now installed.

10/12/2013     02:00:50     UPS: The battery is not installed properly.

10/12/2013     02:00:33     UPS: The battery is now installed.

10/12/2013     02:00:16     UPS: The battery is not installed properly.

10/12/2013     01:59:59     UPS: The battery is now installed.

10/12/2013     01:59:25     UPS: The battery is not installed properly.

10/12/2013     01:59:08     UPS: The battery is now installed.

10/12/2013     01:58:17     UPS: The battery is not installed properly.

10/12/2013     01:58:00     UPS: The battery is now installed.

10/12/2013     01:57:08     UPS: The battery is not installed properly.

10/12/2013     01:56:51     UPS: The battery is now installed.

10/12/2013     01:56:35     UPS: The battery is not installed properly.

10/12/2013     01:56:18     UPS: The battery is now installed.

10/12/2013     01:52:02     UPS: The battery is not installed properly.

10/12/2013     01:51:44     UPS: The battery is now installed.

10/12/2013     01:51:27     UPS: The battery is not installed properly.

10/12/2013     01:51:10     UPS: The battery is now installed.

10/12/2013     01:50:52     UPS: The battery is not installed properly.

10/12/2013     01:50:36     UPS: The battery is now installed.

10/12/2013     01:50:19     UPS: The battery is not installed properly.

10/12/2013     01:50:01     UPS: The battery is now installed.

10/12/2013     01:49:44     UPS: The battery is not installed properly.

10/12/2013     01:49:27     UPS: The battery is now installed.

10/12/2013     01:47:44     UPS: The battery is not installed properly.

10/12/2013     01:47:28     UPS: The battery is now installed.

10/12/2013     01:47:10     UPS: The battery is not installed properly.

10/12/2013     01:46:37     UPS: The battery is now installed.

10/12/2013     01:45:47     UPS: The battery is not installed properly.

10/12/2013     01:36:57     UPS: The battery is now installed.

10/12/2013     01:35:14     UPS: The battery is not installed properly.

10/12/2013     01:34:58     UPS: The battery is now installed.

10/12/2013     01:34:39     UPS: The battery is not installed properly.

10/12/2013     01:34:22     UPS: The battery is now installed.

10/12/2013     01:34:05     UPS: The battery is not installed properly.

10/12/2013     01:33:49     UPS: The battery is now installed.

10/12/2013     01:33:31     UPS: The battery is not installed properly.

10/12/2013     01:33:14     UPS: The battery is now installed.

10/12/2013     01:32:57     UPS: The battery is not installed properly.

10/12/2013     01:32:40     UPS: The battery is now installed.

10/12/2013     01:32:24     UPS: The battery is not installed properly.

10/12/2013     01:11:55     UPS: The battery is now installed.

10/12/2013     01:08:13     UPS: The battery is not installed properly.

10/12/2013     01:07:56     UPS: The battery is now installed.

10/12/2013     01:07:38     UPS: The battery is not installed properly.

10/12/2013     00:06:11     UPS: The battery is now installed.

10/11/2013     23:54:31     UPS: The battery is not installed properly.

10/11/2013     23:54:14     UPS: The battery is now installed.

10/11/2013     23:52:32     UPS: The battery is not installed properly.

10/11/2013     23:38:53     UPS: The battery is now installed.

10/11/2013     23:37:27     UPS: The battery is not installed properly.

10/11/2013     23:35:29     UPS: The battery is now installed.

10/11/2013     23:25:32     UPS: The battery is not installed properly.

10/11/2013     23:24:39     UPS: The battery is now installed.

10/11/2013     22:52:49     UPS: The battery is not installed properly.

10/11/2013     19:24:36     UPS: The battery is now installed.

10/11/2013     19:22:52     UPS: The battery is not installed properly.

10/11/2013     19:22:35     UPS: The battery is now installed.

10/11/2013     19:21:27     UPS: The battery is not installed properly.

10/11/2013     19:20:19     UPS: The battery is now installed.

10/11/2013     19:06:57     UPS: The battery is not installed properly.

10/11/2013     19:06:41     UPS: The battery is now installed.

10/11/2013     18:52:10     UPS: The battery is not installed properly.

10/11/2013     17:57:17     UPS: The battery is now installed.

10/11/2013     17:56:24     UPS: The battery is not installed properly.

10/11/2013     17:56:09     UPS: The battery is now installed.

10/11/2013     17:43:54     UPS: The battery is not installed properly.

10/11/2013     17:33:39     UPS: The battery is now installed.

10/11/2013     17:26:00     UPS: The battery is not installed properly.

10/11/2013     16:56:58     UPS: The battery is now installed.

10/11/2013     16:55:51     UPS: The battery is not installed properly.

10/11/2013     16:54:08     UPS: The battery is now installed.

10/11/2013     16:53:34     UPS: The battery is not installed properly.

10/11/2013     16:34:13     UPS: The battery is now installed.

10/11/2013     16:30:48     UPS: The battery is not installed properly.

10/11/2013     16:13:56     UPS: The output power is now turned on.

10/11/2013     16:01:00     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:59:43     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:58:25     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:57:32     UPS: Failed a self-test.

10/11/2013     15:57:31     UPS: The battery is now installed.

10/11/2013     15:57:15     UPS: The battery is not installed properly.

10/11/2013     15:57:09     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:56:38     UPS: Failed a self-test.

10/11/2013     15:56:37     UPS: The battery is now installed.

10/11/2013     15:56:21     UPS: The battery is not installed properly.

10/11/2013     15:56:00     UPS: Failed a self-test.

10/11/2013     15:55:59     UPS: The battery is now installed.

10/11/2013     15:55:50     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:55:44     UPS: The battery is not installed properly.

10/11/2013     15:54:33     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:53:54     UPS: The battery is now installed.

10/11/2013     15:53:13     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:51:56     UPS: The battery is not installed properly.

10/11/2013     15:50:31     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:49:14     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:47:56     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:46:39     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:45:22     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:44:07     System: Email: Could not mail 'italerts@domain.com'.

10/11/2013     15:43:07     UPS: Failed a self-test.

10/11/2013     15:42:53     UPS: The output power is turned off due to a low battery.

10/11/2013     15:42:52     UPS: At least one faulty battery exists.

10/11/2013     04:08:19     System: Set Date or Time.

10/10/2013     04:07:45     System: Set Date or Time.

10/09/2013     04:07:26     System: Set Date or Time.

10/08/2013     04:07:21     System: Set Date or Time.

10/07/2013     11:10:54     System: Web user 'apc' logged out from 10.10.10.10.

10/07/2013     11:07:52     System: Web user 'apc' logged in from 10.10.10.10.

10/07/2013     04:06:57     System: Set Date or Time.

10/06/2013     04:06:10     System: Set Date or Time.

10/05/2013     23:17:18     System: Email: Could not mail 'italerts@domain.com'.

10/05/2013     23:16:03     System: Email: Could not mail 'italerts@domain.com'.

10/05/2013     23:14:47     System: Email: Could not mail 'italerts@domain.com'.

10/05/2013     23:13:42     UPS: Restored the local network management interface-to-UPS communication.

10/05/2013     23:13:16     System: Network service started. System IP is 10.10.10.10 from manually configured settings.

10/05/2013     23:13:16     System: Warmstart.

10/05/2013     04:05:18     System: Set Date or Time.

10/04/2013     04:05:15     System: Set Date or Time.

10/03/2013     04:04:54     System: Set Date or Time.

10/02/2013     04:04:46     System: Set Date or Time.

10/01/2013     04:04:14     System: Set Date or Time.

09/30/2013     04:03:36     System: Set Date or Time.

09/29/2013     04:02:42     System: Set Date or Time.

09/28/2013     04:02:26     System: Set Date or Time.

09/27/2013     15:45:03     UPS: Passed a self-test.

09/27/2013     15:44:47     UPS: Started a self-test.

09/27/2013     04:02:21     System: Set Date or Time.

09/26/2013     04:01:56     System: Set Date or Time.

09/25/2013     04:01:14     System: Set Date or Time.


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:05 AM . Last Modified: ‎2024-03-12 04:46 AM

0 Likes
0
794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:05 AM . Last Modified: ‎2024-03-12 04:46 AM

Hi Jesse,

No, this is not common. Over the generations of UPS, battery management gets better and better to try and make sure this never happens (hopefully) but we cannot guarantee that due to certain variables (environment, etc). For instance, newer models provide a predicted replace battery date so users can plan ahead for battery replacements before a failure occurs.

This appears to be a catastrophic battery failure and I presume the UPS may be older too (prior to adjustments and tweaks to battery management and trying to prevent this from happening as much as possible).

How old are the batteries? I'd be more concerned if these are like a year old but regardless, it doesn't mean it should happen if they arent. If the batteries are older, it makes a bit more sense since they typically last 3-5 years. Are these in a warm environment (closet, etc)? You could check the NMC data log prior to this event and check the battery voltage and internal temperature of this UPS. This can also expedite this type of problem.

Again, you only see this type of extreme failure when the battery is very hot or very old.

Let me know if you have further questions or want help looking at your data log. Just looking at the event log, it tells me that the battery is very weak and going below a certain voltage threshold where it is constantly not detected/detected.

(Unrelated, I presume your network management card firmware is a little older - I can tell by the wording of the events - if you would like to update it or know more about that, let me know. It won't help with this issue beyond wording of events in the logs).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:05 AM . Last Modified: ‎2024-03-12 04:46 AM

0 Likes
0
795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:05 AM . Last Modified: ‎2024-03-12 04:46 AM

Hi Jesse,

No, this is not common. Over the generations of UPS, battery management gets better and better to try and make sure this never happens (hopefully) but we cannot guarantee that due to certain variables (environment, etc). For instance, newer models provide a predicted replace battery date so users can plan ahead for battery replacements before a failure occurs.

This appears to be a catastrophic battery failure and I presume the UPS may be older too (prior to adjustments and tweaks to battery management and trying to prevent this from happening as much as possible).

How old are the batteries? I'd be more concerned if these are like a year old but regardless, it doesn't mean it should happen if they arent. If the batteries are older, it makes a bit more sense since they typically last 3-5 years. Are these in a warm environment (closet, etc)? You could check the NMC data log prior to this event and check the battery voltage and internal temperature of this UPS. This can also expedite this type of problem.

Again, you only see this type of extreme failure when the battery is very hot or very old.

Let me know if you have further questions or want help looking at your data log. Just looking at the event log, it tells me that the battery is very weak and going below a certain voltage threshold where it is constantly not detected/detected.

(Unrelated, I presume your network management card firmware is a little older - I can tell by the wording of the events - if you would like to update it or know more about that, let me know. It won't help with this issue beyond wording of events in the logs).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore