UPS perfoming warmstarts periodically

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS perfoming warmstarts periodically
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:34 AM . Last Modified: ‎2024-03-14 12:40 AM

0 Likes
5
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:34 AM . Last Modified: ‎2024-03-14 12:40 AM

UPS perfoming warmstarts periodically

I work for a telecommunications company and we use apc ups 3000xl. For the past three days we have been experiencing the ups performing warmstarts periodically. Is this a symptom of a major issue or failure to come or something minor within the ups and NMC?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:35 AM . Last Modified: ‎2024-03-14 12:40 AM

0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:35 AM . Last Modified: ‎2024-03-14 12:40 AM

JonPro,

Yes, I looked at knowledge base article 2572 prior to posting the question in the forum but wanted to see if any one had similar issues and what they may have done to alleviate them. We have two SU3000RMXL3U, one with an AP9617 NMC and the other has an AP9619 NMC. These are both in the same location, wire closet, on different switches and are both experiencing the warmstarts. Our network guy is out until Wednesday so we haven't tried to change port assignments yet but that is an option we have discussed. When he gets back we have also discussed port monitoring for both ups. Should we go ahead and update the firmware before doing any of this?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:34 AM . Last Modified: ‎2024-03-14 12:40 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:34 AM . Last Modified: ‎2024-03-14 12:40 AM

Here are the event and data text files you requested.

The NMC is an APC9617 v3.5.5

I appreciate your help with this matter.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:34 AM . Last Modified: ‎2024-03-14 12:40 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:34 AM . Last Modified: ‎2024-03-14 12:40 AM

Hi Diallo,

Here is a knowledge base article that we hope would help you diagnose/ understand why does an NMC report warmstarts and coldstarts. The knowledge base article ID is 2572, click on the link to open it --> http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2572

Kindly provide the model and serial number of your NMC together with the firmware that is installed on it. It would also help if you could provide the event and data texts/ files of your NMC. In case you are new on getting these files this knowledge base would help you out --> http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9321

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:35 AM . Last Modified: ‎2024-03-14 12:40 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:35 AM . Last Modified: ‎2024-03-14 12:40 AM

i'd also like to make this clear - warmstarts affect only the network management card and not the UPS. it indicates the NMC is rebooting its management interface for one reason or another, per JonPro's post and reference to the knowledgebase article.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:35 AM . Last Modified: ‎2024-03-14 12:40 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:35 AM . Last Modified: ‎2024-03-14 12:40 AM

Thanks Diallo,

Have you looked at the knowledge bases that I've sent? Do you have any other NMC on your end, if you do can you tell us if they are all doing the same thing? Let us start with upgrading your firmware to v3.7.2 here is the guide on how would you do that --> http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=768 and here is the download link for the firmware --> http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SFSUMX372. Is the NMC connected to a router/ switch? Have you tried changing the ports where it is plugged in?

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:35 AM . Last Modified: ‎2024-03-14 12:40 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:35 AM . Last Modified: ‎2024-03-14 12:40 AM

JonPro,

Yes, I looked at knowledge base article 2572 prior to posting the question in the forum but wanted to see if any one had similar issues and what they may have done to alleviate them. We have two SU3000RMXL3U, one with an AP9617 NMC and the other has an AP9619 NMC. These are both in the same location, wire closet, on different switches and are both experiencing the warmstarts. Our network guy is out until Wednesday so we haven't tried to change port assignments yet but that is an option we have discussed. When he gets back we have also discussed port monitoring for both ups. Should we go ahead and update the firmware before doing any of this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore