UPS message below a certain power threshold

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
poofjunior_apc
Crewman
Crewman
0 Likes
2
167

UPS message below a certain power threshold

This was originally posted on APC forums on 3/7/2016


Hello all,l

Our supply voltage (from the wall) is somewhat unreliable such that the UPS consistently switches to battery power for short periods of time. Consequently, we've disabled the "On battery power in response to an input power problem" message,(0x0109) since it occurs quite frequently. However, during a real power-outage, the next level of logging information that we receive is that the UPS is shutting down because the battery charge is too low to support the input load (0x0107). Is there an alert that will send a message based on a configurable battery voltage level? It would be convenient to only receive "on battery power" messages is the battery life is below, let's say 80%, such that we don't constantly get spammed with small fluxes in power.

Thanks!

Tags (3)

Accepted Solutions
poofjunior_apc
Crewman
Crewman
0 Likes
0
167

Re: UPS message below a certain power threshold

This was originally posted on APC forums on 3/8/2016


Many Thanks, Tommy!

This is exactly what I was looking for.

Cheers!

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
167

Re: UPS message below a certain power threshold

This reply was originally posted by Tommy on APC forums on 3/7/2016


Hey Joshua,

One thing that comes to mind as a quick fix would be to enable notification delays for that specific event "on battery in response to an input power problem". I know it's not tied to certain percentage which is what you asked, but if you waited a few minutes, that could allow for small power disturbances to clear (and therefore, no more spamming of emails). You could set the time delay based on your estimated runtime and load to your liking.

Let me know if that option doesn't work for you, but I think this option would be the easiest.

- Tommy

Attachments
poofjunior_apc
Crewman
Crewman
0 Likes
0
168

Re: UPS message below a certain power threshold

This was originally posted on APC forums on 3/8/2016


Many Thanks, Tommy!

This is exactly what I was looking for.

Cheers!